It was a requirement in the 1985 13 section 7-1.2

Garth
----- Original Message ----- 
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, June 10, 2008 8:53 AM
Subject: Re: Hydraulic Data Plate


> The oldest version of NFPA 13 I have is 1989. That requirement was
> included (7-1.2) and was not indicated as a change. I run into
> "missing name plate syndrome" a lot and there is not much you can do
> reliably other than trace the pipe and re-calc, if plans aren't available.
>
>
> At 08:29 AM 6/10/2008, you wrote:
> >Hello sprinklerforum,
> >
> >   When did it the requirement for a hydraulic data plate to be posted
> >   become a part of NFPA 13?
> >
> >   I have a customer that just went through an insurance inspection...
They
> >   wrote them up for not having the data plates posted. This is a 10
story
> >   building and the floors are fed from the standpipe on each floor. The
> >   company that installed the system back in 85 is not to be found
anymore.
> >   The HOA does not want to tear up the units so we can trace the pipe to
> >   reproduce the calcs (or pay what I would charge for that). I'm open to
> >   suggestions. I do have a call in to the AHJ about plans but he does
not
> >   think they exist any more.
> >
> >--
> >Best regards,
> >  Charles Thurston                          mailto:[EMAIL PROTECTED]
> >   Coastal Fire Protection
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to