By 1974 it was in 7-1.2, so I think that if your jurisdiction had adopted a
NFPA 13 1974 or newer it would have been required. Many jurisdictions never
had a formal adoption of 13, they just "Allowed" it to be used when they had
a sprinkler installation, which often allowed it to be used piece meal.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of David Autry
Sent: Tuesday, June 10, 2008 7:59 AM
To: [email protected]
Subject: RE: Hydraulic Data Plate

The requirement is in the 1983 edition, so the requirement was there in
1985. 


It's not in my 1961 edition. So it was added sometime between 1961 and 1983.
LOL

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, June 10, 2008 7:55 AM
To: [email protected]
Subject: RE: Hydraulic Data Plate

It seems that the data plates are often left to the end of the job and
forgotten.  I had one job where the same thing occurred, insurance
inspection and the owner was written up for no plates among other things.
While we were fixing the other deficiencies the owner asked about the
plates, I explained what we would need to do to verify the system data,
which he realized wasn't going to be cheap, and then he asked if we could
just fill something in because the inspector wouldn't know the difference
anyway.  It goes without saying that we did not oblige him in that matter.
We finished the other work and that's the last we heard of the situation.
He probably found some jack-leg that filled out the plates for a couple of
bucks.


I've got a 1989 NFPA 13 and it's in there, 7-1.2


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Tuesday, June 10, 2008 8:29 AM
To: [email protected]
Subject: Hydraulic Data Plate

Hello sprinklerforum,

  When did it the requirement for a hydraulic data plate to be posted
  become a part of NFPA 13?

  I have a customer that just went through an insurance inspection...
They
  wrote them up for not having the data plates posted. This is a 10 story
  building and the floors are fed from the standpipe on each floor. The
  company that installed the system back in 85 is not to be found anymore.
  The HOA does not want to tear up the units so we can trace the pipe to
  reproduce the calcs (or pay what I would charge for that). I'm open to
  suggestions. I do have a call in to the AHJ about plans but he does not
  think they exist any more.

--
Best regards,
 Charles Thurston                          mailto:[EMAIL PROTECTED]
  Coastal Fire Protection

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to