Actually,

The reference to a listed indicating valve being installed 40ft from the 
building "if space permits" is found in the Annex of NFPA-13 and is referenced 
as (1) of the (4) allowable or acceptable valving arrangements from NFPA. It is 
therefore not a requirement of the NFPA standard, just the preferred method of 
the (4) allowable.

There is NO reference anywhere in 8.15.1.1 indicating the use of a curb box for 
fire hydrants only.
Chapter 8.15.1.1 applies to any source of water supply feeding a sprinkler 
system.

The more appropriate (in my opinion) reference would be Section 6.7.1.3 which 
specifically references listed indicating valves.
However, this chapter also allows for the use of a curb box (with key) subject 
to the AHJ.

Following the logic, though NFPA "requires" the use of a listed indicating 
valve, they also ALLOW the AHJ to accept an underground valve with roadway box 
and T-wrench.

To require an additional 200+ft of underground to net a total of 9ft additional 
from the building for the PIV seems, at best, to be complete overkill.

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fire Sprinklers, Inc.
www.waynefire.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, June 18, 2008 1:22 PM
To: [email protected]
Subject: Re: PIV 40ft from Building

I don't have a copy of NFPA 13-2007, but in the 2002 edition, 8.15.1.1 would 
prohibit use of a curb box valve in a sprinkler system supply line.
They would be permissible for hydrant control valves only, right?  If I'm the 
one missing something, let me know.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





Roland Huggins <[EMAIL PROTECTED]> Sent by:  [EMAIL PROTECTED]
06/18/2008 11:13 AM
Please respond to sprinklerforum

To
[email protected]
cc

Subject
Re: PIV 40ft from Building







Mr Frustrated

This requirement has been in standard a long time so without researching it, I 
suspect only Chet Schirmer may know what the committee was thinking.

I have always wondered why we still had it in the standard since it had to have 
been driven from the old days when mainly industrial facilities had sprinklers. 
 It even refers to the plant yard in the text.  It is so seldom used today.  I 
know the DOE plant that I did 5 years of hard time at, there were no PIV's.

Why don't you drop the PIV and just use the curb valve?  IF they really want 
exterior access, put in a wall PIV.

I'll look to see if there is a proposal that we can hang a comment on for the 
ROC meeting.  I don't remember anything touching this so it'll probably be next 
cycle.  Put it on your list of items to submit.

Roland

On Jun 18, 2008, at 7:43 AM, Mark Sornsin wrote:

> Forum:
>
>
>
> Anyone know the reason WHY PIVs are to be located at least 40 ft. from
> the building (on a fire service line piped into the building)?
>
>
>
> I have heard some theories - like to keep the valve free from a
> collapsing wall.  But I am curious if any of you have any definitive
> explanations for that number.  Why not 30 ft.? Why not 50 ft.
>
>
>
> We are dealing with an AHJ who is requiring we pipe an underground an
> additional 200+ ft. around a corner just so our PIV can be at least 40
> ft. from the building.  Otherwise, if we pipe straight out the
> building, the public right-of-way is such that we'd be only 31 ft.
> from the building with the PIV.  This is not good enough for this
> gentleman since, as he says, it is POSSIBLE for you to get it 40 ft.
> away (with the 200+ ft. of underground).  If there was no other way,
> he would have allowed the 31 ft. separation.
>
>
>
> Frustrated-in-Fargo, PE
>
> Fire Protection Engineer
>
> Ulteig Engineers, Inc.
>
> 3350 38th Avenue S.
>
> Fargo, ND 58104-7079
>
>
>
> Direct:    701. 280.8591
>
> Fax:        701.280.8739
>
> Cell:        701.371.5759
>
>
>
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
>
> www.ulteig.com <http://www.ulteig.com/>
>
>
>
> Confidentiality Notice
>
> This message may contain privileged and confidential information. If
> you think, for any reason, this message may have been addressed to you
> in
> error, you   must not disseminate copy or take any action in
> reliance on
> it, and we would ask you to notify me immediately by return email to
> [EMAIL PROTECTED]
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person or entity to which 
it is addressed and may contain proprietary, business-confidential and/or 
privileged material.
If you are not the intended recipient of this message you are hereby notified 
that any use, review, retransmission, dissemination, distribution, reproduction 
or any action taken in reliance upon this message is prohibited. If you 
received this in error, please contact the sender and delete the material from 
any computer.

Any views expressed in this message are those of the individual sender and may 
not necessarily reflect the views of the company.
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

-----------------------------------------------------------------------
    Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into 'The Players Hall of Fame'
       at The Great Games of Business
          http://www.greatgame.com
   Wayne Automatic Fire Spinklers, Inc.
          'Best Places to Work'
       http://tinyurl.com/ov335
      by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to