You can't beat them (that's thwart their efforts or hit them with
sticks) so leave them wet for 24 hrs. Word spreads.
On Mon, Jul 14, 2008 at 12:52 PM, Bobby Gillett
<[EMAIL PROTECTED]> wrote:
Problem; we have some institutional sprinklers in a holding cell at a
local
jail that repeatedly are getting knocked out by the temporary inmates.
Has
anybody come up with a good solution to this problem from our end;
specialty
sprinkler guards or anything?
At the Walla Walla Jail the inmates did the same thing. The solution,
remove the heads, install open heads. Control the water flow with a
solenoid valve. The solenoid valve was controlled by a switch at the day
officers desk. The side benefit was when an unruly inmate was causing
problems, the solenoid valve was opened. I was told cold water lead to a
change in attitude. After the water was shut off, the other inmates
reinforced the lesson.
Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc