Ed,

Two situations in our jurisdiction within 5 years. 

1) 40 Riverside Avenue - 12 Story R2 - Assisted Living- Fire Pump prime
mover burned out during testing, Fire Department Engine tied into FDC
and proximate hydrant, fire watch initiated with radio communications
from the fire command station to the engine operator. Fire Pump restored
and retested appx 4 days.

2) 1 Riverview Plaza - 6 story I2- Hospital - Fire Pump
replacement/upgrade required. Option was a temporary pump or reserve
fire department resources, the latter being chosen as lower cost and
logistically less complicated. Fire Department Engine tied into FDC and
proximate hydrant, fire watch initiated with radio communications from
the fire command station to the engine operator. Fire Pump restored and
retested appx one week.

In both cases a fire protection engineer was employed to survey the
suitability of the existing FDC configuration. Relief for the fire crews
and fuel for the engines arranged. All worked out well.

Hope that helps,

John Drucker
Fire Protection Subcode Official (AHJ)
Firefighter
Borough of Red Bank, NJ


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Friday, July 18, 2008 4:04 PM
To: [email protected]
Subject: RE: FDC Connection

Can any of the current or former fire fighters on the forum give insight
to how often the FDC becomes the sole water supply on a sprinkler
system?  I'm imagining scenarios where a control valve is closed, a
water main is out-of-service, etc.  I'm not asking about manual
standpipes, that's a completely different animal (in regards to the
function of the FDC).

Ed Kramer
Littleton, CO


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to