Ray, Your observation is acknowledged, however there are those that lump all FDC's as supplemental across the board. Maybe this "supplemental" thinking has gone too far.
John ---------------------------- Ray wrote; As a side note, if the FDC is provided specifically for a standpipe or combination standpipe sytem in a "manual-wet" scenario, then it IS designed to provide the full flows and pressures of the standpipe system, keeping in mind the requirement to calculate the demand back to the FDC connection so the piping is sized to overcome the appropriate friction losses and elevations. Always be sure you coordinate the local fire department's ability to provide the required standpipe demands and/or keep the required pressures on the downside of 150 psi at the FDC. Ray Vance Chief Engineering Tech. Wayne Automatic Fires Sprinklers, Inc. www.waynefire.com CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)