Quick question: When you use a single horizontal sidewall sprinkler to cover the area under an open overhead door would you still use the spacing for whatever occupancy is below? If, let's say, this is an Ord Group II hazard this would limit a sidewall sprinkler to 10'x10' - and if I have a 10 ft. door that's 12 ft. wide it would take two sidewall sprinklers to cover uner the door. If this is the case how does this fit into extra hazard occupancies which does not allow the use of sidewall sprinklers? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum