Indeed! Thank you very much!
On 8/8/08, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote: > > See if this is what you're after: > > NFPA-13, 2007 edition, 8.7.3.1.7 states: > > Where sidewall standard spray sprinklers are installed to protect areas > below overhead doors > within ordinary hazard occupancy spaces or rooms, protection area and > maximum sprinkler > spacing for light hazard as specified in Table 8.7.2.2.1 shall be permitted > under the overhead > doors. > > PARSLEY CONSULTING > Ken Wagoner, SET > 760.745.6181 voice > 760.745.0537 fax > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail > www.ParsleyConsulting.com <http://www.parsleyconsulting.com/> < > http://www.ParsleyConsulting.com <http://www.parsleyconsulting.com/>> > website > > > > IPA wrote: > >> Quick question: >> >> When you use a single horizontal sidewall sprinkler to cover the area >> under >> an open overhead door would you still use the spacing for whatever >> occupancy >> is below? If, let's say, this is an Ord Group II hazard this would limit a >> sidewall sprinkler to 10'x10' - and if I have a 10 ft. door that's 12 ft. >> wide it would take two sidewall sprinklers to cover uner the door. If this >> is the case how does this fit into extra hazard occupancies which does not >> allow the use of sidewall sprinklers? >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]> >> (Put the word unsubscribe in the subject field) >> >> No virus found in this incoming message. >> Checked by AVG - http://www.avg.com >> Version: 8.0.138 / Virus Database: 270.5.12/1599 - Release Date: 8/7/2008 >> 8:49 PM >> >> >> >> _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)