See if this is what you're after:

NFPA-13, 2007 edition, 8.7.3.1.7 states:

Where sidewall standard spray sprinklers are installed to protect areas below overhead doors within ordinary hazard occupancy spaces or rooms, protection area and maximum sprinkler spacing for light hazard as specified in Table 8.7.2.2.1 shall be permitted under the overhead
doors.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



IPA wrote:
Quick question:

When you use a single horizontal sidewall sprinkler to cover the area under an open overhead door would you still use the spacing for whatever occupancy
is below? If, let's say, this is an Ord Group II hazard this would limit a
sidewall sprinkler to 10'x10' - and if I have a 10 ft. door that's 12 ft.
wide it would take two sidewall sprinklers to cover uner the door. If this
is the case how does this fit into extra hazard occupancies which does not
allow the use of sidewall sprinklers?
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.12/1599 - Release Date: 8/7/2008 8:49 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to