I have a spec on a project which… well… here it is word for word…

 

…Upon completion of the sprinkler installation, the system shall be
sterilized with an approved chlorinating material before system is placed in
operation.  The amount of chlorine applied shall be such as to provide a
dosage of not less than 50 ppm.  The chlorinating materials shall be
introduced into the water supply lines and sprinkler systems in a manner
accepted by the engineer.  Following a contact period of not less than 8
hours, the chlorinated water shall be flushed from the system with clean
water until the residual chlorine is not greater than 0.4 ppm.  All valves
in water lines being sterilized shall be open and closed several times
during the 8-hour period.

 

I am curious to know if there’s anything regarding the chlorine that could
‘damage’ the components of the sprinkler system.  Having chlorinated water
sitting stagnant at times for 8 hours on the sprinkler seats, etc…  Any
help, NFPA exceptions, guidance would be greatly appreciated!

 

Thanks!

 

RFP Chuck

 