Mike,
Don't forget that unless the home is made out of concrete and steel,
you're most likely going to have to protect the attic space, should
there be one, and that can result in a much larger remote area, limited
sprinkler spacing, and higher starting pressures (see table
8.6.2.2.1a). Also, if you're looking at flowing 90 gallons (900 square
feet x 0.10 gpm) through a 1" water meter you'd be well advised to think
again. Also, remember your minimum water supply duration jumps from 10
minutes (13D), to 60 minutes in NFPA-13.
Lot's to discuss there, and if you'd like to contact me on the phone
I'll be glad to talk over some of the other issues.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
[EMAIL PROTECTED] wrote:
An AHJ wants a 13 system in a 7,300 sqft house because of it's remoteness from
the street. Is the best I can do is calculate 900 sqft because of it being
light hazard with ceilings less that 12' high? Or can I reduce the area more
some how? Please help.
Mike
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.6.6/1621 - Release Date: 8/19/2008 6:53 PM
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)