While Ryan said balancing and as Dave points out is prohibited, that's not
what Ryan means. 

The head in the stack is covering a smaller area and multiplied by the
required density requires much less water out of that head.  Ryan is
certainly allowed to uses whatever orifice size he wants for this purpose.
We regularly mix 11.2 in the booth and 5.6 in the stack or behind the
filter. 

I have been caught using the wrong wording from time to time.  It's
balancing from a layout technician's point of view but not the prohibited
balancing in the code. 

I guess I'm not sure of the location by the description.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Autry, David
Sent: Wednesday, August 27, 2008 12:46 PM
To: [email protected]
Subject: RE: Small orifice sprinkler use in paint booth exhaust duct

14.4.4.6.1
....different orifice sizes shall not be used for balancing the system.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

** Note new email address: [EMAIL PROTECTED]


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan Hinson
Sent: Wednesday, August 27, 2008 12:38 PM
To: [email protected]
Subject: Small orifice sprinkler use in paint booth exhaust duct

Can I use a small orifice head in the exhaust stack of a paint booth in lieu
of 11.2K heads that are in the rest of the booth 14' below to balance the
calcs?  A larger orifice head draws too much water to make the calcs
workable.  NFPA 13(2002) 8.3.4 alludes only to explicitly allowable use in
light hazard occupancies on wet systems.  Does this head have to be an
upright at the top of the stack(which is 4' in diameter, vertically
oriented, and about 11' in length with a rain cover over the top), or can it
be a SDWL installed in the middle or near the bottom?  The required location
this head is driving the whether this system can be wet or not.



Thank you,



Ryan L. Hinson, Nicet III

Design Manager

Fire Construction Design Services, LLC #C124

A Division of Fire Construction Services, Inc.

6950-43rd Avenue SE

St. Cloud, MN 56304

Direct:  320-250-5404

Fax: 320-358-3495

email:   <mailto:[EMAIL PROTECTED]>
[EMAIL PROTECTED]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to