You only need a strainer if the K-factor is LESS THAN 2.8.  You don't
need one for 2.8 or higher.

Paul J. Pinigis, P.E.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, August 28, 2008 2:36 PM
To: [email protected]
Subject: RE: Sprinklerforum Digest, Vol 34, Issue 25 ITEM #1

Right off the top of my head, shiny though it may be in spots, you would
probably lose any gains because you'll need a strainer for a 2.8K head.
Extra pressure loss.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ryan
Hinson
Sent: Thursday, August 28, 2008 11:36 AM
To: [email protected]
Subject: RE: Sprinklerforum Digest, Vol 34, Issue 25 ITEM #1

To all,
" That being said, a 2.8K head
equalizes my calcs better than a 5.6K head does. Can I use one that
small?