If you've installed it per the mfgr. listing, as it was tested, then where's 
the heartburn.  Don't deviate or improvise the installation and TYCO should 
stand behind the product.

You can't design a system to operate perfectly in every single "what-if" 
scenario.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, October 01, 2008 11:42 AM
To: [email protected]
Subject: RE: Window Sprinklers

And nobody thinks that might be a problem? I have installed these heads four 
feet below a ceiling and outside with only the mullion to act as a heat 
collector. Seems like quite a leap of faith to assume the sprinkler will 
activate in a timely manner.

Ron Fletcher



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Wednesday, October 01, 2008 8:29 AM
To: [email protected]
Subject: RE: Window Sprinklers

Yes.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Wednesday, October 01, 2008 8:10 AM
To: [email protected]
Subject: RE: Window Sprinklers

So the test assumes the glass remains intact until sprinkler activation?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Wednesday, October 01, 2008 7:28 AM
To: [email protected]
Subject: RE: Window Sprinklers

The window sprinkler was tested using the exact same criteria as is used
to establish any other rated assembly.   A test fire is built on one
side of the subject and burned for the duration of the rating and then there's 
a steady-stream hose test (not entirely sure if that's of the same duration - 
Drucker, chime in now please) during which water is jetted against the subject 
and it can't fail.  I think your assumption is correct that the surface is 
protected so long as the sprinkler(s) flow at their minimum required rate - 15 
or 20 GPM depending on spacing.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, October 01, 2008 6:43 AM
To: [email protected]
Subject: RE: Window Sprinklers

Just a guess but I think the window damage (without the sprinkler
protection) would occur within the first minutes.  Once the minimum water 
discharge is established I would assume the protection would last as long as 
the water is flowing.  Does this sound logical?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: Window Sprinklers
From: "Bill Minkel" <[EMAIL PROTECTED]>
Date: Wed, October 01, 2008 9:27 am
To: <[email protected]>

Ahhhhh, Gotcha

Bill Minkel, Designer
Dallas, TX
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, September 30, 2008 3:16 PM
To: [email protected]
Subject: RE: Window Sprinklers

Of course it's MORE than adequate for a 1 hr wall, the question was is there a 
"Less" that would work for 1 hr, but not 2 hr? Maybe a smaller orifice or 
totally different head or even a vert. sidewall? Hence "Window Sprinkler Lite"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Tuesday, September 30, 2008 11:29 AM
To: [email protected]
Subject: RE: Window Sprinklers

Educate me here, I would have thought that a wall assembly rated for 2 hours 
would also be more than adequate for 1 hour?

Bill Minkel,

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to