Forum members,

 

We too, have the Tyco WS model sprinkler 'system' available here in
Australia and currently I believe it is the only Fire Rating Level (FRL)
'listed' (read approved by TESTING) sprinkler for this use. Although the
sprinklers are expensive the R&D behind them and the inherent 'listing' to
achieve a FRL is what you are paying for (and probably the Tyco insurance
premium that goes with them). Any other sprinkler manufacturers on track to
get a listed FRL sprinkler in the marketplace?

 

With the relatively recent allowance of 'fire engineering' here in Australia
we have had to complete some project designs (particularly before the Tyco
WS release) where lengths of glazing were protected, but we could never
provide a design 'fire rating'. These projects were completed in conjunction
with all design team members and generally led by the fire engineers who can
account for a wetting density, usually per m2, required to remove an agreed
heat level. They also make other design requirements including glass type,
thickness, etc.

 

The Achilles' heel in the Tyco sprinkler (no offence to Tyco but the
construction reality) is its inability to be used on anything but fixed
framed glazing systems. As an example many retail projects are consistently
requiring the aesthetic beauty of glazed separation of areas between the
retail and carparking areas, which are usually required to be 'fire
separated' in Australia. Essentially these glazed entry areas don't work
well without doors..   

 

From a sprinkler designer point of view I put forward a couple of my
comments/opinions for the like minded forum members,

 

-       Almost all fire engineers restrict combustibles from close proximity
of the glazing - if your project does not seem to be complying with this,
ask questions. This is particularly applicable with carparking as a car fire
can be shielded from the normal occupied space sprinkler system.

-       Glass ain't glass apparently. Toughened seems to be the glass type
of choice due to higher tolerance to exposure when dry, wet and as it is
getting wet.

-       Not all your discharge will make it to the windows - in fact the
percentage is probably lower than you expect. Better to underdo the
percentage than overestimate when hydraulically calculating sprinkler
discharges. Although airborne water particles absorb radiant heat if you are
trying to wet glass I prefer a sprinkler that emits water more specifically
towards the glazing and not in a 360 degree pattern.  

-       Try and use the lowest operating temp and RTI sprinkler suitable.

-       Don't forget to wet the framing materials - not much point having
glazing between concrete slabs to have the glass fall over because the
frames burn away. They should be non-combustible - but hey, stranger things
have happened. 

-       Try and avoid all horizontal mullions unless you can locate a
sprinkler below them (Tyco WS understandably prohibits them). This has been
very difficult in practice particularly if you have a doorway such as a
sliding door to a retail area (yep had to do one of those - try telling the
team that the door should be separated and/or rated) and the auto door
hardware is typically right above the door. In this particular case I
located the HSW pendant to spray as much water below the door head - not
perfect but better than nothing. Also don't forget to ensure any auto doors
close from fire system trip. You can't 'drench' an opening.

-       From my on site testing the longer glass panes tend to 'rivulet'
unless the over glass flow is quite high (sorry I don't have figures on
this). I did find the use of a spray pattern which throws not only high on
the window but also longer down the glass (a bit like rain) seems to assist
with reducing these dry spots which I associate with surface tension issues.
Any scientific analysis of this members?  

-       SSP sprinklers mounted pendant are not effective in providing
wetting to the high level corners of the windows - avoid using them for this
application. Horizontal Side Wall mounted pendant (facing the glazing
system) are quite effective for this. 

-       I have NEVER completed a drencher test without some form of
obstruction getting stuck in and deforming at least one of the sprinkler
patterns. Make sure the water supply is clean and flushed!

-       If at all possible (i.e. no water and drainage issues) complete a
drencher test to check your design and installation. Taking a number of
different sprinkler types to try during a test can be very enlightening and
may prove fruitfull.

-       Although mentioned above that there are no FRL guarantees, avoid
obvious flaws such as a 1 hour tank supply is not much good if the fire
engineer has asked for 2 hours of continuous protection.  

-       Make sure the owner/builder/interior decorator etc. knows that
NOTHING can be placed between the sprinkler and the glass. No, not even
Venetian blinds! (certifiers note: look at the system when re-certifying)

-       You will be surprised how NOT water proof some glazing systems are
under pressured sprinkler streams - be vigilant for window leaks during a
test on the DRY side.

-       They are usually ugly - tell the architect to get over it or use
fire rated glass - he'll come round.

 

I would be more than happy to get experienced feedback from other
designers/installers on this issue to add to the knowledge base, either on
or off forum whatever suits.

 

....oh and watch out for escalator pits near your drencher test. They make
for very expensive swimming pools. :-(

 

 

Regards,

Mark Cummings

Sydney, Australia

[EMAIL PROTECTED]

  

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Wednesday, 1 October 2008 12:39 AM
To: [email protected]
Subject: RE: Window Sprinklers

 

Yep, that's what I'm saying.  Of course there are other ways to skin this

cat.  Fire rated glass is a $$$$ option but I think the size of each pane is

limited so it wouldn't be confused with a glass wall.  This would be code

compliant. 

 

Perhaps an alternate method of compliance is possible with ordinary heads

but that's between the designer of responsibility (EOR) and the AHJ.  Note

I'm trying to keep the PE part to a minimum because I know reality sometimes

leaves these things in your lap.  And an alternate is not the same as code

compliance technically, practically maybe but not technically.  

 

I'd say a side light with an ordinary head might be something as an AHJ I'd

entertain as equivalent.  A 60' wall not a chance.  Also I required the

glass wall of this size to be valved separate from the rest of the system

all the way back to the header.  Our approval was based on the fact

traditional fire rating is not lost when the sprinklers are shut off for

maintenance or TI's.  There is no reason to lose the rating just because

sprinklers (Tyco) are being used instead of sheetrock.      

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [EMAIL PROTECTED]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Russell

Sent: Tuesday, September 30, 2008 8:59 AM

To: [email protected]

Subject: RE: Window Sprinklers

 

Let me see if I understand Chris, from an architectural standpoint, the

glass wall is not a rated wall unless the Tyco sprinkler is used?

 

 

"Cause there is nothing in the code that I am aware of that gives a rating

with ordinary sprinklers at any spacing."

 

 

"If you have a corridor that requires a rating Tyco heads are the

only code complying solution I am aware of if using sprinklers." 

 

Chris Cahill, P.E.

 

 

 

Russell Rewis

Brown Automatic Sprinklers, Inc.

107C Hemlock Street

Valdosta, Georgia 31601

229-244-8130

[EMAIL PROTECTED]

 

 

_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [EMAIL PROTECTED]

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 

_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [EMAIL PROTECTED]

 

To Unsubscribe, send an email to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to