2006 IBC 704.12 provides for exterior window opening utilizing a water
curtain.  "Exception - Opening protectives are not required where the
building is protected throughout by an automatic sprinkler system and
the exterior openings are protected by an approved water curtain using
automatic sprinklers approved for that use." The sprinklers and the
water curtain shall be installed in accordance with section 903.3.1.1
(NFPA13) and shall have an automatic water supply and fire department
connection."

The Tyco/Central WS for example is a listed window sprinkler. ICC ES
Legacy Report NER-516 provides specific instructions on the application
of window sprinklers including but not limited glazing, frames, non
bearing walls, etc. The complete report can be downloaded/read at; 
 
http://www.icc-es.org/reports/pdf_files/NES/NER516.pdf
 
John Drucker
Fire Protection Subcode Official (AHJ)
Red Bank, NJ


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Wednesday, October 01, 2008 10:28 AM
To: [email protected]
Subject: RE: Window Sprinklers

The window sprinkler was tested using the exact same criteria as is used
to establish any other rated assembly.   A test fire is built on one
side of the subject and burned for the duration of the rating and then
there's a steady-stream hose test (not entirely sure if that's of the
same duration - Drucker, chime in now please) during which water is
jetted against the subject and it can't fail.  I think your assumption
is correct that the surface is protected so long as the sprinkler(s)
flow at their minimum required rate - 15 or 20 GPM depending on spacing.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, October 01, 2008 6:43 AM
To: [email protected]
Subject: RE: Window Sprinklers

Just a guess but I think the window damage (without the sprinkler
protection) would occur within the first minutes.  Once the minimum
water discharge is established I would assume the protection would last
as long as the water is flowing.  Does this sound logical?

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: Window Sprinklers
From: "Bill Minkel" <[EMAIL PROTECTED]>
Date: Wed, October 01, 2008 9:27 am
To: <[email protected]>

Ahhhhh, Gotcha

Bill Minkel, Designer
Dallas, TX
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, September 30, 2008 3:16 PM
To: [email protected]
Subject: RE: Window Sprinklers

Of course it's MORE than adequate for a 1 hr wall, the question was is
there a "Less" that would work for 1 hr, but not 2 hr? Maybe a smaller
orifice or totally different head or even a vert. sidewall? Hence
"Window Sprinkler Lite"

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill
Minkel
Sent: Tuesday, September 30, 2008 11:29 AM
To: [email protected]
Subject: RE: Window Sprinklers

Educate me here, I would have thought that a wall assembly rated for 2
hours would also be more than adequate for 1 hour?

Bill Minkel,

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com



__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3485 (20081001) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to