I'd love to hear your logic on that interpretation.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (FAX)


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of danarbel
Sent: Tuesday, November 04, 2008 3:48 PM
To: [email protected]
Subject: RE: ESFR Heads below obstructions

Well, I read all that and it seems that all you need are 12 heads 

Dan


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: 04 November, 2008 7:28 PM
To: [email protected]
Subject: ESFR Heads below obstructions

Dan,

All references here are from the '07 edition of NFPA-13:

14.4.4 Where ESFR sprinklers are installed above and below obstructions, 
the discharge for up to two sprinklers for one of the levels shall be 
included with those of the other level in the hydraulic calculations.

15.4.4 Where ESFR sprinklers are installed above and below obstructions, 
the discharge for up to two sprinklers for one of  the levels shall be 
included with those of the other level in the hydraulic calculations.

16.2.3.5 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations

16.3.3.6 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

17.2.3.4 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

17.3.3.5 Where ESFR sprinklers are installed above and below 
obstructions, the discharge for up to two sprinklers for one of the 
levels shall be included with those of the other level in the hydraulic 
calculations.

22.4.4.6.4 The requirements of 22.4.4.6.1 to include every sprinkler in 
the design area to be included in the system discharge shall not apply; 
where ESFR sprinklers are installed above and below obstructions, the 
discharge for up to two sprinklers from one of the levels shall be 
included with those of the other level in the hydraulic calculation.

Based on what I read in the ROP just published it doesn't look like any 
of these have been removed, although it appears that the wording in 
22.4.4.6.4 has been moved around a bit, and a new 22.4.4.6.4.1 has been 
added (See 13-462, Log CP82 in the ROP)

Hope that is what you were after.
*
*PARSLEY CONSULTING

Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



danarbel wrote:
> Question regarding the number of ESFR heads required for hydraulic calc. 
>
> The nominal number is 12. 
>
> There was a requirement to add 2 heads if there are heads installed below
> beams or AC ducts. 
>
> If I'm not wrong the addition of 2 heads was abolished. 
>
> Please confirm or correct me,
>
> Dan Arbel
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com 
> Version: 8.0.138 / Virus Database: 270.8.6/1765 - Release Date: 11/3/2008
4:59 PM
>
>
>   
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


__________ NOD32 3580 (20081103) Information __________

This message was checked by NOD32 antivirus system.
http://www.eset.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to