Brian,

8.15.10.3 2007 ed.  Talks about the criteria you must have to eliminate 
sprinklers from an electrical room.  The NEC prohibits running piping in the 
dedicated electrical space 110.26 2008 ed.

8.15.3 2007 ed. Discusses stairways.  Not sure what you are looking for.  IBC 
1020.1.2 2006 ed. Discusses acceptable penetrations in stairway enclosures.

Hope this helps.