Rick: If the AHJ would read the direct code, it would be apparent that the "Dedicated Space" is not defined by floors walls and ceiling, but by the amount of space required around above and in front of electrical equipment, If this is less than the total room, then there is room to run all of those other systems in and out of the electrical space/room in that area other than the zone. As I've said before there is a very good drawing of this in the handbook.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matsuda, Richard Sent: Wednesday, December 17, 2008 8:58 AM To: [email protected] Subject: RE: Electrical Rooms Craig, See NFPA-70, Article 110.26 (I) (a) for Indoor Installations. This describes the 'dedicated electrical space'. "No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone". Some AHJ's interpret this section to say that the sprinkler piping is allowed to end in the room, but the piping passing thru the room to another area is "foreign" to the electrical installation. Ask your AHJ what is his interpretation of this. There is also a subsection (c) which allows sprinkler protection in the dedicated space provided it complies with the section. rick matsuda _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)