Malleable fittings can fail for a multitude of reasons.  Lines installed out of 
square in such a way that the fitting is stressed, fitting was dropped, bad 
casting, etc.

Sloped lines over time have a tendency to get "unsloped", especially in venues 
where there may have been modifications to the sprinkler systems over the 
years.  Low points are created, systems are not completely drained and the 
first long freeze and you've got the makings of a big ICEE machine.

Also any lines that may come in contact with operating machinery that can setup 
vibrations or other harmonics in the sprinkler system.  When connecting to big 
air compressors for instance vibrations from the air compressor can transfer to 
the sprinkler system piping and cause small fittings to fatigue.  

Or there's the other factor of another discipline doing work and hanging on a 
sprinkler line and twisting a fitting.  A small leak becomes bigger until you 
finally get that very special call at 4am.

The ice blockage doesn't always grow in a logical manner.  It depends on where 
it starts, pitch of pipe, fittings, where the source of water is originating, 
blockage within the pipe from other matter, or other factor causing resistance 
to migration of the ice formation where it can't grow longitudinally.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Smith, Steven D. 
(CSFD)
Sent: Wednesday, December 17, 2008 12:56 PM
To: [email protected]
Subject: RE: Dry Pipe System Dilemmas

One break occurred in the drum drip of an unheated warehouse (self explanatory 
as you mentioned). The other break appeared to occur at an elbow where the 
horizontal pipe turned vertical in an combustible concealed attic space. I 
didn't look at it personally so I'm not sure if the pipe was completely 
horizontal or if there was enough slope to it to collect water at the elbow. My 
guess is there was enough slope to it.

Next question... How much condensation can form on the insides of DP systems? 
Let say for conversation, a gallon of H2O collects in a location that isn't 
drained out. I know water expands when it freezes, but wouldn't the expansion 
take place back in the "dry" portions of the system? I mean unless there was 
enough water there to hold things from expanding into the system and cause them 
to expand outward, the water "should" expand into the dry portions of the 
system.... Shouldn't it?
Path of least resistance.

Steve

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, December 17, 2008 9:01 AM
To: [email protected]
Subject: Re: Dry Pipe System Dilemmas

Where did the breaks in the system occur?  That may help in diagnosing the 
problem.  In a previous life we had a dry system that froze and broke at the 
drum drip due to lack of maintenance (also the drum was in an unheated space).  
We had another where there was over 100 low point drains in an attic system and 
one may have been missed during maintenance / after testing (I think we ended 
up tagging 156 low point drains after that happened).  There is always some 
water in the systems, if they are not maintained properly things can happen.

Andrew Weisfield

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to