The anti-freeze is a good idea but one that is outdated. Water purveyors do not 
permit additives in sprinkler systems.  

Forest Wilson 
Cherokee Fire Pro 
Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Dave Sornsin" <[email protected]>

Date: Wed, 17 Dec 2008 18:11:20 
To: <[email protected]>
Subject: RE: Dry Pipe System Dilemmas


Dear Forum:

Here's some input from a former sprinkler guy who saw his share of
freeze-ups for obvious reasons (see address below). 

1. I never had a problem with riser mounted air compressors because they
were typically only on small systems that didn't have accelerators.
2. I'm convinced that dry pipe valve trippings can be caused by accelerators
with clogged diaphragm holes on systems where the air pressure fluctuates.
The air pressure fluctuates on systems with tankless air compressors.
3. Take apart an accelerator and look at the size of the inner workings
including diaphragm and hole. Now picture, cruddy, rusty, scaly sprinkler
water in this accelerator. Some (all?) have anti-flooding devices so the
water doesn't get in there, but often they don't work.
4. You're asking for a freeze up if you ever do a full flow trip test in the
fall. 
5. In the humid Midwest, it's amazing how much water is pumped into old,
large dry systems - especially if you don't have an air compressor with
tank. 
6. Sell your customers on spring trip tests and return trips in the fall to
blow out low points.
7. If it's a problem drum drip in a cold area, consider adding a few ounces
of anti-freeze after blowing it out in the fall.
8. Most busted drum drips were at the lower valve (see 7)
9. Ideally the owner blows out any cold exposed drum drips until that part
of the system is froze. Since this doesn't happen, and you're still blamed,
consider item 7.
10. Dryers or Nitrogen will dramatically extend the life of all dry systems.
A tank mounted air compressor will at least pull some of the water out of
the air (are your fitters draining the tanks at each inspection?). 
11. Roll-grooved pipe causes mini-dams that also trap water (that one was
for Mr. Church and anybody else on this Forum in 1996). 

Dave Sornsin
General Manager
Nardini Fire Equipment
 
303 20th St N
Fargo, ND 58102
701.235.4224
fax 701.235.5089
cell 701.371.0643
 
[email protected]
www.nardinifire.com
 
 


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to