Has anybody had the opportunity to seismic brace a 13R cpvc system in
platform style construction?  Recently a designer in my company submitted
plans for a NFPA 13R system built of platform style construction: TJI's for
the ceiling / floor assemblies and gang-nailed truss for the roof component,
the AHJ asked where the seismic braces were?  The system was supported with
"offset" style hangers in the floor joist cavity and 2-hole strap hangers on
top of the bottom chord of the roof trusses in the attic portion.
Ultimately we braced this system utilizing a brace manufactured by AFCON -
expensive and labor intensive.  I can't find any exemptions in the codes
(IBC, IFC, etc) for deleting the seismic bracing for this application, 13R
say's Hanging and Bracing is to be in compliance with NFPA 13, common sense
say's this piping and hanging scenario is sufficient provided the pipe is
supported per its listing.  Does anybody have any ideas? 

 

 

Jim Johnston, P.E.