I'm sure the ME's tried to put more on the drawings, but since they knew so 
little of what was actually required it probably WAS worthless.

I've been confused on that issue too, how can someone who has never designed a 
system know if what was submitted is right or not?  I've had to provide some 
really dumb details for PE's who didn't know how to read a sprinkler piping 
plan simply because they were the EOR and had to approve my shop drawings.

My favorite is the Archyteck approving fire protection shop drawings.  
Fortunately the building was mostly office space and not anything real exotic 
but he still missed a few things and since no one follows up during 
construction maybe it was corrected maybe not.  No one knows.  Depends if the 
mechanical  inspector knew his job or not.

Everything else you said is spot-on.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Wednesday, January 07, 2009 1:14 PM
To: '[email protected]'
Subject: RE: another fire - this will be interesting

I may have shared this before:  I once talked with an architect from an A/E 
firm about this issue.  He said that their MEs have tried to put more detail on 
sprinkler drawings before, but the contractors always change it citing code 
requirements, so it's a waste of time.  I sometimes wonder if that guy 
understood how profoundly ridiculous that 'problem' really is.

When it comes to justifying up-front engineering by the engineer of record 
(only in THIS industry would we make a statement like that!), you have to be 
able to explain the benefits associated with the additional engineering costs. 
And the engineer has to be able to perform to a level that justifies the 
additional expense. There is more than design time savings incurred by the 
contractors when the engineer actually completes a good layout as part of the 
A/E package. There's the radical reduction in unknowns - and associated CYA 
price tag. And yes, the engineer HAS gone out on a limb, so if the design has 
to be significantly changed by the contractor, a change order will be coming 
and is rightly warranted.

In the end, if an engineer can't design a system, then how can they approve 
someone else's design.  If they can't design a system they are violating their 
ethics when they include fire sprinkler in their design package. But we all 
know that...  >>sigh<<

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591
[email protected]




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Paul Pinigis
Sent: Wednesday, January 07, 2009 10:46 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

The lack of detail on the engineer's sprinkler drawings is often dictated by 
the client, not the A/E firm.  For example, the Navy will not allow us to do 
detailed designs because they (like many others) believe that will lead to 
change orders.  Somehow they don't have a problem with the HVAC engineer or the 
plumbing engineer showing their detailed designs.  I would like to see equal 
treatment; the HVAC engineers should show a hatch pattern on the floor plan 
with a note that says "deign ductwork to provide a comfortable environment.".

Paul Pinigis, P.E.
Life Safety Department Head



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, January 07, 2009 10:57 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

You'll have to do more than just make your magical FPE's appear from the sky, 
you'll have to change the mindset of an entire industry.

For too long the A/E industry has felt it was a waste of time and money to do 
detailed design for fire protection, the thought being that since the 
contractor did all that for free, why duplicate the effort.  Less hours spent 
on fire protection meant more hours to be used by someone else or could be 
saved altogether.  That makes the PM look good, hours unspent=bigger bonus.

So even if you did have your super FPE's appear, they would still not be able 
to produce the documents the contractors would love to see.

Trying to educate project managers, schedulers, department managers etc...... 
is an uphill battle.  They don't understand the FP industry, how it works, who 
does what, submittals to AHJ's, minimum information required on a drawing 
package, when in the course of the project fire protection needs to start and 
finish, what info is needed to do the fp design work (when you are doing more 
than an "X" on a drawing, and the list of obstacles goes on and on.  Next 
project, you start the battle all over again.

Other disciplines don't understand the rules you have for head spacing, 
deflector distances below decks, obstructions, water pressure and flow issues, 
etc. Most think FP as being able to move where ever so they have more room and 
are often told that very thing by their supervisors.

You don't know how many times I've been told by ME's who are supposed to be 
responsible for FP work that it is so confusing.  What's scary is most probably 
know just enough to pass the FPE.  So that's obviously not the answer to the 
overall problem.




Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, January 06, 2009 11:24 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

We'd need several hundred qualified FPEs (or equal) to fall out of the sky in 
order to do what you  say, as desirable a concept as you present.
That and a couple thousand more so we contractors can put them on staff so we 
can evaluate water supplies and perform hydraulic calculations in accordance 
with the SFPE White Paper (unless the more recent revs have allowed us to calc 
systems like we've been doing as an industry since there were calcs).

Instead we have FPE-Plumbing Designer ACTING like FPEs despite being only 
casually familiar with our industry, codes, standards, materials,
etc.- i.e., practicing outside their area of competence.

And so we don't just call this PE bashing, I'll point out that contractors 
evaluating water supplies- and that would be all of us performing calcs based 
on some flow test, ours or someone elses- need to be aware of lowest tank 
gradient, the importance of correcting for elevation and other corrections 
needed to move the data correctly from the test to the floor flange. I have a 
project where my competitor doing an adjacent building on same site off same 
main is using a flow test result that is 10 PSI higher than mine, with twice 
the flow. I've become familiar with the site, water supply, and did a more 
accurate test than they did, I guess that's the price of being able to sleep at 
night.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Paul Pinigis
Sent: Tuesday, January 06, 2009 10:35 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

Very well said John.  This is exactly the approach that we take; we look at the 
building or project holistically and our fire protection engineers direct the 
architect, mechanical, electrical, structural, telecom, etc. to ensure 
coordination and compliance.

Paul Pinigis, P.E.
Life Safety Department Head

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520
d:(804) 521-7011

http://www.haengineers.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Tuesday, January 06, 2009 9:46 AM
To: [email protected]
Subject: RE: another fire - this will be interesting


Simply put "fire protection" is not seamless. Often enough it's a patchwork of 
pieces and parts assembled without a clear and common objective. We see this 
everyday with smoke detectors being installed in unsprinklered elevator 
hoistways because no one told the alarm engineer that sprinklers had been 
eliminated by the sprinkler engineer, or fire dampers installed in one hour 
walls in fully sprinklered buildings because no one told the mechanical 
engineer. The disconnect with the fire service is yet another example, site 
planning left to the civil engineer without regard to fire protection needs.

What we need are MEPF firms, engineering firms that employ and fully utilize 
fire protection engineers to look at the big picture, assess, plan, design, 
coordinate and supervise cost effective and efficient fire protection solutions.

If as a fire protection engineer you're simply designing fire alarm or 
sprinkler systems you are not working to your full potential !  There are firms 
that provide life safety analysis to provide passive fire protection solutions, 
often coined working for the "dark side" they nonetheless do what others are 
not, looking at the big picture. High rise sprinklers in Chicago or San Diego 
anyone ?

So how does the active fire protection community counter this claim, perhaps by 
long term planning, synergistic value driven engineering. It goes all the way 
back to codes and standards, how many cycles did it take to recognize 
sprinklers in fully sprinklered buildings for notification survivability on 
fire alarm systems ?

One stop shopping ladies and gentlemen, one stop shopping.

Sincerely

John Drucker
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Monday, January 05, 2009 10:36 AM
To: [email protected]
Subject: RE: another fire - this will be interesting

Ron said "(I suspect the savings in mains, hydrants, fire stations, apparatus 
and firefighters is way more than a wash in fully sprinklered, planned 
communities than the cost of sprinklering schools)."

Were these savings realized?  Last I read which was a long time ago there was 
very little saved on the reduction in the list you provided.
They never actually followed through in reducing mains and limiting stations 
etc.  I will certainly say in the macro scale these saving are not being fully 
realized.  Hell we still have fully paid stations in many departments that 
average < 1 call a day and plenty more that are < 2.  As a pay-per-call 
volunteer I saw more fire than many paid guys in these parts.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [email protected]

Mail: P.O. Box 69
        Waverly, MN 55390

Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Friday, January 02, 2009 2:05 PM
To: [email protected]
Subject: Re: another fire - this will be interesting

Good point so far overlooked. There's also the dubious "saved foundation" 
success that may have not been worth the risk of going into harm's way. And no 
one has brought up the environmental advantages of sprinklers--less smoke, less 
destroyed building materials to dispose of, less dirty water to process and, of 
course, less water used overall. And the Scottsdale less public money spent on 
firefighting infrastructure (I suspect the savings in mains, hydrants, fire 
stations, apparatus and firefighters is way more than a wash in fully 
sprinklered, planned communities than the cost of sprinklering schools).

On Fri, Jan 2, 2009 at 11:49 AM, Dave <[email protected]> wrote:
> Since we are offering up various thoughts and theories on the general
application of sprinklers .....  Regardless of how much egress time is 
allegedly available or occupant ability to respond or even construction 
materials & methods - there still is a fire in a building -  Presuming we get 
everyone out safely and that eliminates the 'life safety need for sprinklers' 
will we then NOT call the fire department to respond??
>
> Once there's a fire in a building there is another completely real
> life
hazard in play - the responding emergency personnel.  Some may enter the 
building and be very close to harm's way and others may respond and have 
ancillary functions - traffic control, EMS, crowds etc.  Regardless of the 
specifics we can generally agree that a fire in a non-sprinklered building will 
be larger than the same fire in a sprinklered building.
It's not always the fire but medical emergencies or trips & falls that create 
the threat of harm.  The larger the fire the greater its duration and intensity
- all of which increase exposure and life safety risk to responders.
>
> Personally I don't get behind the non-combustible and limited or low
> fuel
load argument as a valid application of sprinkler omission.  Maybe thats just 
my narrow focus or perhaps its because I've been to alot bigger fires in 
non-sprinklered buildings than sprinklered buildings.  The closer you get to 
the gun - the bigger the bullet.
>
> Thanks & Happy New Year
> Dave P.
> Fireman first and always.
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to