"He installed the UG system without calling for any inspection.........."

Frankly you'd be digging this thing up in my jurisdiction and here's what
I'd cite;

N.J.A.C. 5:23-2.18 Inspections

(b) Inspections during the progress of work: The construction official and
appropriate subcode officials shall carry out periodic inspections during
the progress of work to ensure that work inspected conforms to the
requirements of the code.

(c) Notice for inspection:

1. The owner or other responsible person in charge of work shall notify the
enforcing agency when the work is ready for any required inspection
specified herein or required by the construction official or appropriate
subcode official. This notice shall be given at least 24 hours prior to the
time the inspection is desired. This notice shall represent an attestation
on the part of the owner, other than single-family owner-occupants
performing their own work, or other responsible person in charge of work,
that the work has been completed in conformance with the code and is ready
for inspection.

2. Inspections shall be performed within three business days of the time for
which it was requested. The work shall not proceed in a manner which will
preclude the inspection until it has been made.
 
Sorry George but this whole thing stinks. Unfortunately the AHJ is looking
in NFPA-24 when he/she should be looking in the administrative provisions of
the jurisdictions construction code.

Lastly the "Grapevine has it that there was a leaking 90 below a
lead-in-Instead of fixing prior to hydro, they cut in a valve and shut it
off." Constitutes concealment and deception and with that grounds for
revocation or suspension of license in my state.

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Red Bank, NJ



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, February 26, 2009 5:44 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: AHJ right or wong?

No.
And there's a host of baggage with the site guy.
That's why we ended up doing the flushing, and why we're testing.
He installed the UG system without calling for any inspection so AJ cannot
verify leakage at joints, thrust blocks/megalugs, depth of bury.
Grapevine has it that there was a leaking 90 below a lead-in-
Instead of fixing prior to hydro, they cut in a valve and shut it off.
So I've acknowledged the baggage, but point to a narrow focus despite
whatever else has occurred:
GC hired us to test per #24.
We did and passed with 14 gal allowable leakage when allowance was 72.

So the question remains 
Does the IFC wording 
Test per #24 AND AS ACCEPTED BY THE LOCAL AHJ 
Mean he picks criteria from #24 or does he witness and accept the procedure
we choose?

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
bver...@comcast.net
Sent: Wednesday, February 25, 2009 10:27 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: AHJ right or wong?

Did the U/G contractor test with the joints exposed? 

Bruce Verhei 

763-658-4483 
763-658-4921 fax 

Email: chr...@sentryfiremn.com 

Mail: P.O. Box 69 
Waverly, MN 55390 

Location: 4439 Hwy 12 SW 
Waverly, MN 55390 
-----Original Message----- 
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church

Sent: Wednesday, February 25, 2009 1:32 PM 
To: sprinklerforum@firesprinkler.org 
Subject: RE: Spkr Save 

About to get in pssing contest with local AHJ on UG test per #24. 
We sprinklered an 833,000 sf ESFR box, didn't do UG loop. 
Site guy couldn't get test to pass with hydrants closed. 
We were asked to help, and I suggested testing with hydrants open. 
We did that and it passed, only 1/3 allowable leakage allowed. 
However, the local AHJ is refusing to pass it, saying he wants it re-tested 
with hydrants closed the way it went initially. 

I'm about to ask him where he sees that in #24; but the following wording 
"and as approved by the fire code official" in the IFC (see below) might 
give him a leg to stand on. Can any of you agree or disagree? 

Would the below require a local amendment be in place? 
My retainage of >$100k, not to mention the GC's, is hanging in limbo. 

>From IFC 2006 
901.5 Installation acceptance testing. 
Fire detection and alarm systems, fire-extinguishing systems, fire hydrant 
systems, fire standpipe systems, fire pump systems, private fire service 
mains and all other fire protection systems and appurtenances thereto shall 
be subject to acceptance tests as contained in the installation standards 
and as approved by the fire code official. The fire code official shall be 
notified before any required acceptance testing. 

George Church' 
Rowe Sprinkler 
g...@rowesprinkler.com 
570-837-7647 


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to