The applicable #24 is crystal clear in giving us the option to test with
hydrants open or closed, and increases allowable leakage if hydrants are
open. 

Ok, so its 2-0 that the IFC wording means he witnesses the test, not
determines the criteria (absent local amendments).

Now that its just a word problem, any AHJs want to agree? If you don't want
to agree, one dissenter's enough!  (seriously, I come here for all sides).

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: Wednesday, February 25, 2009 3:46 PM
To: [email protected]
Subject: RE: AHJ right or wong?

Then additional to my first email that's the designer's choice it sounds
like.  AHJ's don't get to choose the methods if more than one is provided in
code or a standard.  Read the fine print on this - make sure the standard
allows either open or closed in this case.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, February 25, 2009 2:11 PM
To: [email protected]
Subject: RE: AHJ right or wong?

Allowable leakage in NFPA #24 is calculated on #joints, valves, and if you
have dry-barrel hydrants open, you get more allowable leakage. So the
allowable leakage is (from memory) 11 gallons in 2 hours with the hydrants
closed; 82 gallons with the hydrants open.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, February 25, 2009 2:56 PM
To: [email protected]
Subject: RE: AHJ right or wong?

Explain what you mean by hydrants closed and open?  What exactly was opened
and closed.  Are you saying there was too much leakage in the system with
the hydrant control valves closed?  This is the pressure test?




Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, February 25, 2009 2:46 PM
To: [email protected]
Subject: AHJ right or wong?

(changed subject from spkr save. BTQW I went to the fire scene, I felt like
a proud parent of the system that worked this AM)

About to get in pssing contest with local AHJ on UG test per #24.
We sprinklered an 833,000 sf ESFR box, didn't do UG loop.
Site guy couldn't get test to pass with hydrants closed.
We were asked to help, and I suggested testing with hydrants open.
We did that and it passed, only 1/3 allowable leakage allowed.
However, the local AHJ is refusing to pass it, saying he wants it re-tested
with hydrants closed the way it went initially.

I'm about to ask him where he sees that in #24; but the following wording
"and as approved by the fire code official" in the IFC (see below) might
give him a leg to stand on. Can any of you agree or disagree?

Would the below require a local amendment be in place?
My retainage of >$100k, not to mention the GC's, is hanging in limbo.
 
>From IFC 2006
901.5 Installation acceptance testing.
Fire detection and alarm systems, fire-extinguishing systems, fire hydrant
systems, fire standpipe systems, fire pump systems, private fire service
mains and all other fire protection systems and appurtenances thereto shall
be subject to acceptance tests as contained in the installation standards
and as approved by the fire code official. The fire code official shall be
notified before any required acceptance testing.
 
George Church'
Rowe Sprinkler
[email protected]
570-837-7647

 


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to