Thanks for the vote of confidence, I was somewhat taken back when I got home
and opened this package.
I've worked in plenty of small towns where they don't have trained plan
reviewers.
I've even had AHJ's confess they don't understand and asked if I can walk
them through it.
I once spent 2 hours with a Deputy on a lodging house retrofit and we became
best buddies, did his first barrel test, patted each other on the back
afterwards.
I don't know if it was because the Owner and I were calling in for status
one a week after waiting 6 weeks for permit or what.
I plan to drive out and see the Chief and go over these with him personally
and just ask him who did the review.
I'm sure it wasn't the State, they have some rally sharp guys and also the
resources of WPI in Worcester.
I might ask for a re-review with them as I'm holding up a job in a bad
economy and effecting many more people than myself.
Not to mention I'm now LAST on the job, I have no coordination from other
trades and have to work around everything.
I almost started writing a reply last night but glad I didn't now.  ;-)
We change codes tomorrow, all current editions but at least the building
permit was issued last November.  Whew!
Tom

-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of Parsley
Consulting
Sent: Sunday, March 01, 2009 10:20 AM
To: [email protected]
Subject: Re: Hydraulics


Tom,

At first glance my thought is that the reviewer has some sort of mental
problem.  I'm certainly not the authority on how to conduct yourself in
a business environment, however in the past 20 years I've performed
close to 5,000 plan reviews and never have I even dreamed of making such
an insulting remark on a set of comments.  Whoever it is has behaved in
an unprofessional manner, and such behavior has no place in that
position.  Of course, I've said a number of things like that while doing
reviews just to get that thought out of my system, but I'd never dream
of making my official review comments take on a personal nature.

As to the accuracy of his remarks, I can only say that what you've
described as your process sounds accurate to me, particularly if you've
accounted for all the fittings where the water is making a change in
flow direction.  I don't understand his comment regarding where certain
fittings have to be placed in various segments, perhaps because I don't
have a set of plans to see what he's talking about.  It does seem to me
as though this is very heavy handed, almost as though something was
under his skin before he sat down to look at your drawings and calcs.

The one comment you've included which bothers me to the point where I
think you have to raise a serious protest about it is the remark
regarding the hose stream.  It would seem that his remarks are ignorant
of the process involved in adding hose demand to calculations, as noted
in NFPA-13, sections 11.1.5.4 and 11.1.5.5(1-3).  I can't even wrap my
thoughts around why you'd have to take into account an inside hose
demand when there are no inside hose valves.

As for his comment regarding the demand from all your flowing sprinklers
having to be based on the most demanding protection area there are no
words which are vulgar enough to describe how far from reality this is.
>From what you've described it sounds as though you're flowing the proper
water for each coverage area for each sprinkler.  Based on what you've
described you're using residential sprinklers, and it sounds to me as
though you've followed the two methods for establishing demand shown in
11.3.1.2 (1 and 2).  I agree that you'll certainly have balancing in the
calculations which will push up the flow from the lesser demanding
sprinklers, but there's nothing in any text I've read which makes the
claim he's nailing you with.

Quite frankly, Tom, I'd insist on a meeting and go over this.  The AHJ's
I work with out here would never stand for me making remarks of that
nature to anyone, and if I were to do so I'd be looking for another
review client fairly quickly.

Hey, maybe you could ask for the arrogant horse's butt to provide you
with the name of the individual who taught HIM calculations to see if
you could help him get his money back because that individual failed
miserably at the task.

Just some thoughts on a lovely March morning here in California.

Keep us posted, huh?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Tom Duross wrote:
> Preface: I'm a self taught hydraulic calculation dweeb and I always
thought
> I had a handle on the basics.
> I also should take the hydraulics course on-line, not a plug but I'm sure
> there's a lot I don't know.
>
> I got a written review of a set of plans and calcs I submitted by mail
> today.
> The AHJ's reviewer is anonymous and mails his reviews via the AHJ.  First
> for me and that's fine.
> It's a 4 unit attached residential building.  Full Basements, 775 SF/flr,
2
> floors with a small loft, attached garages.
> Single 2" copper supply to a doghouse on the end, single zone system,
steel
> in the basement, cpvc upstairs.
> Just a description of the system as it bears little to my questions, but
> good for background.
>
> Comment #1 states my calculations are completely wrong.  No citing of
> section, just wrong.
> He backs it up by saying that I include the downstream fitting in each
> segment and I should be including the fitting at the start of the segment.
> I've just opened this up and I'm stunned.  He goes further to ask where my
> training is in hydraulics and who (by name) taught me.  Not nice in my
book.
> Let me explain how I do these and would you kind folks (and George too)
tell
> me if I'm off-base or not.
>
> My first segment is the underground.  2" copper, annealed, 1 piece from
the
> corporation stop on the main up into the doghouse.
> I input 34' of type L, a gate valve and a 90 degree elbow with the tap as
> the inflow.  I know it's closer to 30' and the tubing is rolled and
unrolled
> so I really have a l o n g  sweep but I usually go a little conservative.
> He says I have to include the tee.  I disagree in principle for now.  My
> next segment is the compression fitting (I actually braze a male adapter
on)
> to a 90 to a 2" horizontal backflow with ball valves (all copper because
> it's still potable).  I input a 1' of vertical, a 90, 1' of horizontal
> copper, 2 ball valves and use 8 psi for the backflow non-linear loss
> (guessing at the time but checked and adjusted for the basement demand of
> 150 gpm) and put a 100 gpm (inside and/or outside) hose demand at the
elbow.
> He says the base elbow must be included but says the hose demand should be
> after the backflow.  There are no hose valves, why?  Anyway.. Fast forward
> to the last segments where again he says I'm incorrect, again.  I show
7.5'
> of 1" cpvc, and elbow and a head with 224 SF of area on it.  He says I
have
> to include the branch tee feeding it but I included that in the segment
> feeding that segment!  Am I doing this all wrong?
>
> Another thing.  I have a 4 head and a single head calc. (plus the basement
> and garage).  I always used to do this when they had separate demands and
I
> just still do but that's not my question.  I have 4 heads with different
> areas being served by each.  2 are in bedrooms, 212 SF and 224 SF, one in
a
> hall with 90 SF and one in a walk-in closet with 56 SF.  He says they all
> have to "provide the same density at similar dimensions".  WTF!  I have to
> base all 4 heads (or all heads in the building for that matter) based upon
> my most demanding head which is the 224 SF bedroom that is 16x14 using
16x16
> flow and pressure requirements for all 4 heads.  I've got almost a
gallon/sf
> in the closet and that's incorrect according to my reviewer.
>
> I'm not going to start a reply now as I just poured three fingers of
single
> malt but more because I want to re-read his comments and see what you
folks
> think.
> I submitted these on Dec. 10th and I'm getting angry phone calls because
we
> haven't started yet and I get home and find this monkey-poop (ok, I'm
> sipping now).
> Have I been doing these wrong all this time?  There's some more but I'm
> starving.
> Dazed and confused.
>
> Tom Duross
> Go Red Sox!
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to