Per NFPA 13, 2007: 21.20.19.2 Installation Requirements. 21.20.19.2.1 In buildings sprinklered in accordance with NFPA 13, closets less than 12 ft2 (1.1 m2) in area in individual dwelling units shall not be required to be sprinklered. Closets that contain equipment such as washers, dryers, furnaces, or water heaters shall be sprinklered regardless of size. [101:30.3.5.4] Previously, in areas where I have done work that did not recognize the Life Safety Code, we could not use this wording to eliminate sprinklers in small closets in apartment buildings. Basically, NFPA 13 said it could only be eliminated in hotels / motels: 8.15.8.2* Closets and Pantries. Sprinklers are not required in clothes closets, linen closets, and pantries within dwelling units in hotels and motels where the area of the space does not exceed 24 ft2 (2.2 m2), the least dimension does not exceed 3 ft (0.9 m), and the walls and ceilings are surfaced with noncombustible or limited-combustible materials. So, even if the LSC is not recognized in an area, can you still take the exception noted above in Chap 21 and eliminate sprinklers in small closets since it is now part of the body of NFPA 13? Please feel free to call if you have any questions or comments. Travis Mack, SET _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected]