Travis,

I would agree. I see where everything under section 21.20 is bringing in
the language from the Life Safety Code.

Cliff,

I know that you were asking about 13R closets the other day; apparently
101 was what we were thinking about when we wanted to add sprinklers
when it included the water heaters.


Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis
Mack, SET
Sent: Tuesday, March 03, 2009 5:26 PM
To: [email protected]
Subject: small closets NFPA 13

Per NFPA 13, 2007:
 
21.20.19.2 Installation Requirements.
21.20.19.2.1  In buildings sprinklered in accordance with NFPA 13,
closets
less than 12 ft2 (1.1 m2) in area in individual dwelling units shall not
be
required to be sprinklered.  Closets that contain equipment such as
washers,
dryers, furnaces, or water heaters shall be sprinklered regardless of
size.
[101:30.3.5.4] 
 
Previously, in areas where I have done work that did not recognize the
Life
Safety Code, we could not use this wording to eliminate sprinklers in
small
closets in apartment buildings.  Basically, NFPA 13 said it could only
be
eliminated in hotels / motels:
 
8.15.8.2* Closets and Pantries. Sprinklers are not required in clothes
closets, linen closets, and pantries within dwelling units in hotels and
motels where the area of the space does not exceed 24 ft2 (2.2 m2), the
least dimension does not exceed 3 ft (0.9 m), and the walls and ceilings
are
surfaced with noncombustible or limited-combustible materials.
 
So, even if the LSC is not recognized in an area, can you still take the
exception noted above in Chap 21 and eliminate sprinklers in small
closets
since it is now part of the body of NFPA 13?
 
Please feel free to call if you have any questions or comments.
 
Travis Mack, SET
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to