Steve,

As you pointed out, "for certain purposes". 509.2 stipulates the purposes;

509.2 Group S-2 enclosed or open parking garage with Group A, B, M, R or S
above.

"A basement and/or the first story above grade plane of a building shall be
considered AS A SEPARATE AND DISTINCT BUIDLING FOR THE PURPOSE OF
determining AREA LIMITATIONS, CONTINUITY OF FIRE WALLS, LIMITATION OF NUMBER
OF STORIES and TYPE OF CONSTRUCTION when all of the following conditions are
met;"

IBC 509.2 does not state for the purpose of occupancy classification, thus
it is still a mixed use building. Only two things separate structures into
wholly separate buildings 1) Fire Walls, 2) Distance.

With that said 903.3.1.2 is clear; 

[F] 903.3.1.2 NFPA 13R sprinkler systems.
WHERE ALLOWED in BUILDINGS of GROUP R, up to and including four stories in
height, automatic sprinkler systems shall be installed throughout in
accordance with NFPA 13R.

What we are speaking of is Buildings of Group R and something else other
than an incidental use.

The proposed scope of 13R makes it clear that 13R is not for mixed use
buildings;

"1.1* Scope. This standard shall cover the design and installation of
automatic sprinkler systems for protection against fire hazards in
residential buildings up to and including four stories in height."

If the intent is to allow 13R systems in the residential portions of a mixed
use building, whether a 508 or 509, then the IBC needs to be amended
accordingly. 

Sincerely

John Drucker
Fire Protection Subcode Official
Building/Fire/Electrical Inspector

Safe Buildings Save Lives !


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Friday, March 13, 2009 5:12 PM
To: [email protected]
Subject: RE: Mixed-Use Code Question

I agree with you, and the TC on Residential Sprinkler Systems has adopted
language for Chapter 1 of 13R that is intended to finally clarify the
appropriate application of the standard.   If ratified at the code hearing,
the standard will be applicable buildings of residential occupancy and their
accessory non-residential uses only; the only way that a single structure
would have sprinkler systems designed to different standards is if it is
fire-separated to the extent that the areas are considered separate
buildings in accordance with the building code for that construction type.
These separations may be horizontal and/or vertical.
 
I've tried to transcribe Log #21, proposal 13R-2 below:

Revise the scope of NFPA 13R to read: 

"1.1* Scope. This standard shall cover the design and installation of
automatic sprinkler systems for protection against fire hazards in
residential buildings up to and including four stories in height."

Revise A.1.1 as amended by Proposal 13R-58, Proposal 13R-57, & Proposal
13R-56, to read as follows: 

"A.1.1 NFPA 13R is appropriate for use only in buildings that are entirely
residential occupancies up to and including four stories in height.
Residential occupancies are defined in this standard.  The height of the
building is as defined in the applicable building code. It is the intent of
this standard that if NFPA 13R is appropriate for use, that it be used
throughout the entire building. It is recognized that incidental and
accessory areas, as defined by the applicable building code, might exist
within that residential occupancy. Such incidental and
accessory areas would typically be considered by the applicable building
code to be part of the residential occupancy and subject to the requirements
for the residential occupancy by.  Where buildings are greater than four
stories in height, or where buildings are of mixed use, such buildings
should be protected throughout with NFPA 13.  Where structures of mixed use
can be totally separated so that a residential occupancy is considered a
separate building under the applicable building code, NFPA 13R can be used
in the building of entirely residential occupancy while NFPA 13 is used in
the other building(s).  (Examples of incidental and accessory occupancies
found in residential occupancies can include: management offices,
private parking garages/areas within a dwelling unit, community laundry
rooms, clubhouses, exercise facilities, tenant
storage within a dwelling unit, etc.).

Note, a separated mixed use structure (separated by fire-resistance rated
assemblies) is not the same as a structure with separate buildings
(separated by fire walls). However, there may be applicable building code
provisions that permit upper and lower portions of a structure, separated by
a three hour fire rated horizontal assembly, to be considered as separate
buildings for certain purposes (See 2006 NFPA 5000, Section 7.4.3.6.5 and
2006 IBC Section 509.2)."


Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Friday, March 13, 2009 12:51 PM
To: [email protected]
Subject: Re: Mixed-Use Code Question

Although I disagree with interpretation for horizontal fire barriers
that Jamie refers to that has been typical in many jurisdictions out
on the best coast. As others have mentioned typically the entire lower
floor is commercial with 13/horizontal fire barrier/13R above.

On Fri, Mar 13, 2009 at 10:27 AM, Jamie Seidl <[email protected]>
wrote:
> In IBC land, there is Separated and Non-separated mixed use. Non
separated, your entire building would be full 13.  In separated mixed use,
as long as the ratings meet the required separations or "separate buildings"
of the code, (including horizontal) you can use 13 for the lower area and
13R for the upper.  There has been some contention on the designation of a
separate building and a horizontal fire barrier, but this configuration has
met the intent of the code in the jurisdictions I've dealt with.
> Jamie Seidl
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Tom Duross
> Sent: Friday, March 13, 2009 12:23 PM
> To: [email protected]
> Subject: Mixed-Use Code Question
>
> I have a question about a small project I'm bidding and how it relates to
> other's building codes.
> Four storey 8 unit residential building, in bid stage, just got
notification
> that one unit, half the ground floor, will be zoned for commercial use.
> I'm at odds if this changes the building to mixed-use or not.  I've asked
> the gc if he's still applying as an R2 and he's not sure, architect in on
> vacation (go figure).  I'm leafing through our building code (ICC-03)
right
> now to see if this qualifies as ancillary with regards to design (13 vs.
> 13R) but I just thought I'd ask the masses with a little time on their
hands
> how this would resolve under their current codes.  Often we have similar
> provisions and interpretations and I don't have the workbook, tabs or
> supplement yet for ours.  We're new to this edition.
>
> I'm able to refer to 13 for design in areas like Basements but still base
> the remainder of the system under 13R requirements and our old code gave
> little guidance as to percentages with regards to areas outside of the use
> group.  I'm wondering if, disregarding permit application for now, the
> addition of one of the 8 units from residential use to commercial use
(will
> be a store) will effect the design.
>
> Tom
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature
database 3935 (20090313) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to