How many floors and is the sprinkler system separate or combined with the standpipes?
Standpipes can feed sprinklers but you must provide a control valve and check valve at each connection, or you can run a separate sprinkler riser. Steve L. >From The Road Sent from my Verizon Wireless BlackBerry -----Original Message----- From: "Nick Melosi" <[email protected]> Date: Sun, 15 Mar 2009 15:20:50 To: <[email protected]> Subject: Manuel Wet Standpipe Do you need four control valves and Check valves on a manual wet standpipe and sprinkler system? 1. Riser 2. Sprinkler System 3. Standpipes (2) You need to be able to work on the sprinkler system and standpipes separately. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum <http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum> For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3937 (20090314)__________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com <http://www.eset.com> _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)