How many floors and is the sprinkler system separate or combined with the 
standpipes?

Standpipes can feed sprinklers but you must provide a control valve and check 
valve at each connection, or you can run a separate sprinkler riser. 

Steve L.
>From The Road


Sent from my Verizon Wireless BlackBerry

-----Original Message-----
From: "Nick Melosi" <[email protected]>

Date: Sun, 15 Mar 2009 15:20:50 
To: <[email protected]>
Subject: Manuel Wet Standpipe


Do you need four control valves and Check valves on a manual wet standpipe 
and sprinkler system? 
1. Riser 
2. Sprinkler System 
3. Standpipes (2) 
You need to be able to work on the sprinkler system and standpipes 
separately. 