What Steve said.
3 floors but the ahj is requiring a standpipe. It is Manual. On Sun, Mar 15, 2009 at 7:20 PM, <[email protected]> wrote: > How many floors and is the sprinkler system separate or combined with the > standpipes? > > Standpipes can feed sprinklers but you must provide a control valve and > check valve at each connection, or you can run a separate sprinkler riser. > > Steve L. > >From The Road > > > > Do you need four control valves and Check valves on a manual wet standpipe > and sprinkler system? > 1. Riser > 2. Sprinkler System > 3. Standpipes (2) > You need to be able to work on the sprinkler system and standpipes > separately. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)