Yes we have many dry systems. I have never seen one which does not have a pressure regulator and an adjustable PRV. Most of the adjustable PRV's are set to relieve any pressure which is 10-15 psi above the set pressure.
Rodney K. Hamm, P.E. President/Owner Falcon Fire Protection Office (478) 953-1677 Cell (478) 396-6988 Date: Thu, 19 Mar 2009 08:47:08 -0500 From: "Dave Sornsin" <dsorn...@nardinifire.com> Subject: RE: Excessive system pressure To: <sprinklerforum@firesprinkler.org> Message-ID: <a584babd8c23482ea2c0dd60d1182...@daves> Content-Type: text/plain; charset="us-ascii" Rodney: Just curious. I'm guessing there's gotta be a few dry systems down there in unheated warehouses with extreme temp swings. So in these systems with 100% air, do you find the pressure above the dry valves climbing to extreme levels in the summer? Dave Sornsin General Manager - Fargo Office Nardini Fire Equipment _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: techsupp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)