I FULLY INTEND THAT THIS WILL BE MY LAST POST REGARDING THIS SUBJECT. I promise 
to make a concerted effort to make this statement true. I would also like to 
state that you should probably read this entire post if you have not completely 
tuned out regarding this subject!


I obtained my Bachelors Degree in Mechanical Engineering and I am also a FPE; I 
am fully aware and I understand thermal expansion. A few forum participants 
posted data regarding water, but refrained from including any thermal expansion 
data for air. My point is that thermal expansion effects both water and air. 
The following two paragraphs were copied from the
internet:


Charles's law states that when pressure is kept constant, there is a direct 
relationship between volume and temperature. As a gas heats up, its volume 
increases, and when it cools down, its volume reduces accordingly. Thus, if an 
air mattress is filled in an air-conditioned room, and the mattress is then 
taken to the beach on a hot day, the air inside will expand. Depending on how 
much its volume increases, the expansion of the hot air could cause the 
mattress to "pop."


 

That is to say, he discovered that if a container of air were to be sealed at 
0*C, at ordinary atmospheric pressure of 15 pounds per square inch, and then 
heated to 100*C but kept at the same volume, the air would now exert a pressure 
of about 20 pounds per square inch on the sides of the container.
(Of course, strictly speaking, the container will also have increased in size, 
that would lower the effect-but it's a tiny correction, about ½% for copper, 
even less for steel and glass.)  Remarkably, if the air were initially at a 
pressure of thirty pounds per square inch at 0*C, on heating to 100*C the 
pressure would go to about 40 pounds per square inch-so the percentage increase 
in pressure was the same for any initial pressure: on heating through 100*C, 
the pressure would always increase by about 33%.

 

Water on the other hand: On heating from 0*C through 30*C, the pressure will 
stay essentially constant, while heating from 30*C through 100*C, the pressure 
will increase by about 4%. Check out the thermal expansion properties of air 
and water if you think I am wrong. Web site:
http://www.engineeringtoolbox.com/water-thermal-properties-d_162.html 

 

In summary, I guess I am simply trying to state that trapped air pockets will 
create a more significant pressure increase or decrease in a closed sprinkler 
system than water when the temperature changes. 

 

I will absolutely admit that I cannot explain mathematically why we see such 
drastic pressure increases in the numerous wet sprinkler systems where we have 
identified and resolved these issues (based strictly on Charles's Law, the 
pressure increases should not be so extreme), but I can state that the 
excessive pressure problem is completely resolved after we bleed off a 
significant amount of the trapped air pockets. This is not a theory, this is 
absolute real world action with undeniable results. Some systems relieve air 
for 20-40 minutes through multiple sprinkler heads (loosened enough to hear and 
feel the air escape from the system at the various high points). After we 
remove a significant amount of the trapped air, the problem is resolved.
And to address the obvious question, the problem is resolved even without a
175 psi PRV (we do not always provide the 175 psi PRV, but we typically 
recommend them for gridded systems; some clients agree to provide them, but 
some decide against paying for the 175 psi PRV).

 

I will officially let it go. I have planted a few seeds through this forum and 
hopefully caused a few people to think about the subject to some degree.


 

I sincerely hope that I have not caused any animosity or hurt feelings..if so, 
PLEASE know that I had no intentions of making anyone feel bad in any way, 
shape or form. 

 

I also feel compelled to state that I am really not trying to win an 
argument....arguing or an obsession of being right is usually a fruitless and 
ultimately negative exercise. That being said, I imagine that I am now 
officially "branded" as argumentative and/or obsessive. I hope this is not the 
case, but I am a "Big Boy" and I can deal with it I guess! Over time, I 
sincerely hope everyone on this forum will realize that my overall intentions 
are to have a positive impact, learn from the forum participant's experiences 
and share a few of my personal experiences along the way! 

 

Take care,

 

Rodney K. Hamm, P.E.
President/Owner
Falcon Fire Protection
Office  (478) 953-1677

Cell  (478) 396-6988

 

Date: Thu, 19 Mar 2009 09:26:38 -0500

From: "Chris Cahill" <[email protected]>

Subject: RE: Excessive system pressure

To: <[email protected]>

Message-ID: <4ea8e8951e2342039812650e425c4...@chris2005>

Content-Type: text/plain;     charset="us-ascii"

 

I find it VERY interesting that you find it VERY interesting there has been

no findings. Hint of insecurity in your position?  

 

Why would anyone try your experiment when it is irrelevant to the constant

volume container of a sprinkler system? 

 

No one "believes water compression" is responsible for anything.  It's

thermal expansion without compressible air.  

 

"Or could it possibly be that water and air act differently to temperature

changes in Georgia than any other place in the world?"  I guess that's as

valid a theory as trapped air causes excess pressure.  I have only driven

through the great state of Georgia once so I'll defer to your expertise on

matters in Georgia.   

 

You have made an extraordinary claim thus it is incumbent upon you to

provide extraordinary evidence.  Your claims go against the text book

('02-7.1.2.2, A.7.5.3.2 and the handbook) and the vast field experience of

this forum. There's even the fancy math thingies with letters, subscripts

AND symbols which us PE's like.  

 

I have the upmost confidence in my position so I'm not in any big hurry to

propose and try a valid model experiment of the situation.  If I had doubts

it would be a higher priority.  Given a choice I'll spend my time with

friends and family.  When those priorities allow (and I have my Guitar Hero

fix for the day) you'll get feedback.   

 

And as far as your trees and grids.  Sure sounds like what 7.1.2 describes.

Imagine that the trees are OK and the grid is not and that's what the text

book covers. Coincidence I'm sure.  Granted I concede once text books had

the center of the universe as Earth and the Earth was flat.  I'd like to

think we've come a long way and today's text couldn't be that wrong. But hey

those that wrote those old texts probably thought the same thing, they

couldn't be that wrong.  Good news if you are right we'll probably name the

principal after you.  Bernoulli, Pascal, Hazen-Williams, Hamm!

 

If you believed your theory why are you recommending the PRV?  Shouldn't

removing the air only be what you would advocate?  If the PRV wasn't

required when installed then it was and still is code compliant.  Why would

you need both seemingly counter solutions?     

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to