Rodney,

Last week when I posted on the incompressibility of pure water (14.7 psi 
to reduce volume 1 part in 5x10^7) illustrated through a hypothetical 
temperature swing from 40F to 80F, I thought my statement of BIG 
PRESSURE was self explanatory on the massive pressure increase water can 
impart on piping.  Let me now exchange "BIG PRESSURE" for two-million 
four-hundred seventy-two thousand three-hundred sixty-nine psi (2,472,369).

So in a worst case situation of pure water filling 100% of a fixed 
volume rigid system, the temperature does not need to rise much at all 
to get a 100, 200, or 300 psi increase in system pressure.

Now let's take a 100% air filled dry pipe system.  With an air regulator 
set at 50 psi and a temperature swing from -20F to 120F (244K - 322K), 
pressure will increase to 50 * 322 / 244 = 66 psi. Barely past the PRV's 
setting.

I suspect the prv's on the dry pipe system are more about water delivery 
time then over pressurization protection.  In short, the gridded systems 
experiencing over pressurization only need a prv not air-bleed valves.

Don't confuse thermal expansion and compressibility.  These are two 
different properties and it is the incompressibility property of liquid 
water that makes big problems out of a tiny amount of thermal expansion.

Trevor Spain
Fire Pro Corporation
404 N Cedar
Shelbyville, IL  62565

Rodney Hamm wrote:
> Wow what a week..I was at another plant yesterday which has the same exact
> problem. This facility has 14 wet systems fed by a fire pump so the static
> pressure is maintained by a jockey pump at 170 psi. Several systems had
> system pressures >175 psi. One of the gridded systems had a system pressure
> downstream of the alarm check valve of 205 psi just before lunch. At 4:00
> PM, the system pressure downstream of the alarm check valve was well above
> 300 psi (the system gauge was pegged so I do not really know the actual
> pressure). Riser nipple arrangement on the near main and the far main. The
> ITC for the system was attached to the bottom of the far main (in other
> words, essentially the same as for the facility I visited on Tuesday). This
> system was also installed prior to the NFPA requirement of a 175 psi PRV for
> all gridded systems. I have recommended the provision of a 175 psi PRV,
> installing air bleed off valves and removing a significant amount of the
> trapped air from the system. BTW, my client specifically requested that we
> install a 175 psi PRV on the remaining 13 systems as a precautionary
> measure; this approach might be considered unnecessary, but the PRV's will
> not cause any detrimental effects and we will ensure the system pressures
> for all 14 systems do not exceed 175 psi. 
>
>  
>
> Response to questions posted by Chris Cahill: Removal of the air would
> resolve the excessive pressure problems; however, I still recommend the
> provision of a 175 psi PRV (regardless of the "grandfather rule") because it
> is required by NFPA and I believe it is in the best interest of my client.
> As long as we provide the 175 psi PRV, any future high pressure incidents
> will be immediately and automatically resolved. If the system is drained and
> reinstated in the future (by plant employees or some other company which
> does not bleed off the trapped air pockets), the system will more than
> likely experience the same or similar high pressure problems due to the
> trapped air pockets, so in my opinion the PRV is justified as a long term
> and more permanent resolution of the problem.
>
>  
>
> Rodney K. Hamm, P.E.
> President/Owner
> Falcon Fire Protection
> Office  (478) 953-1677
>
> Cell  (478) 396-6988
>
>  
>
> Date: Wed, 18 Mar 2009 21:22:44 -0400
>
> From: "Rodney Hamm" <[email protected]>
>
> Subject: Excessive system pressure
>
> To: <[email protected]>
>
> Message-ID: <[email protected]>
>
> Content-Type: text/plain;     charset="us-ascii"
>
>  
>
> On a more serious note, I was at another plant yesterday which has the same
>
> exact problem. This is really why I am writing this email. Warehouse with 1
>
> gridded system and 7 tree fed systems. The problem only exists for the
>
> gridded system; the remaining 7 systems had nominal pressure differences
>
> (0-10 psi difference) between the top & bottom gauges. On the gridded
>
> system, the public pressure upstream of the alarm check valve was fairly
>
> steady all afternoon at ~60 psi. At 1:50 PM, the system pressure downstream
>
> of the alarm check valve was 190 psi. I described the problem to the plant
>
> engineer and he wanted me to explain the problem to the plant manager. The
>
> three of us returned to the riser at 2:10 PM and the system pressure
>
> downstream of the alarm check valve was already up to 205 psi. We have not
>
> even entered our really hot days of summer yet! Riser nipples on the near
>
> main and the far main and the ITC for the system was attached to the bottom
>
> of the far main (in other words, the auxiliary or low point drain was
>
> converted into an ITC by installing the base of a sprinkler head at the end
>
> of the pipe and then someone placed an ITC sign on the valve). This system
>
> was installed prior to the NFPA requirement of a 175 psi PRV for all gridded
>
> systems. I have recommended the provision of a 175 psi PRV, installing air
>
> bleed off valves and removing a significant amount of the trapped air from
>
> the system. 
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 8.0.238 / Virus Database: 270.11.21/2014 - Release Date: 03/20/09 
> 06:59:00
>
>   