If they are actually separated by "fire walls", and not just fire-rated
walls, then they are separate buildings per the IBC.  But, yes, you can
use one riser to feed both buildings provided that you protect the
connecting pipe from freezing temperatures and you do not exceed the
maximum allowable area for the system.  

Paul Pinigis, P.E.
Life Safety Department Head




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 10:05 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Possible IBC question

The buildings are actually just additions to an existing building and
they
are separated by two adjacent fire walls.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084
-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Paul
Pinigis
Sent: Monday, March 23, 2009 10:03 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Possible IBC question

It depends upon the distance between buildings and the percent of open
wall space under the roof.  

Paul Pinigis, P.E.
Life Safety Department Head




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen
Purvis
Sent: Monday, March 23, 2009 9:07 AM
To: sprinklerforum@firesprinkler.org
Subject: Possible IBC question

I am looking for some code help. According to NFPA 13 8.2.4 you can have
separate buildings that share a common roof, walls or passageway be
protected by one riser. Does anyone know if the IBC contradicts this? I
have
an architect telling me I have to have a separate riser for each section
of
building. They claim that I can have the risers in the same room but
that
each building section must have a separate riser.

Karen Purvis
Senior Designer
Facility Systems Consultants
713 South Central Street,
Suite 101
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to