That 150 foot rule seems to be pretty standard in Washington and
arrives at being enforceable through the path David describes.

On Wed, Apr 8, 2009 at 9:43 PM, Smith, David (VFD)
<[email protected]> wrote:
> I would always recommend asking for the reference when you receive comments 
> and aren't sure where they are coming from. You'll want to make sure that you 
> know what they are referencing and even that they have the ability to enforce 
> it.
>
> For instance, portions of Chapter 5 of the 2006 IFC pertaining to fire 
> department access weren't adopted at the state level and isn't enforceable in 
> WA unless the local jurisdictions adopt it through local ordinance or have 
> their own requirement. Other agencies may modify the model code with 
> something more specific or restrictive. Our reference here in Vancouver would 
> be:
>
> Vancouver Municipal Code 16.04.160, Amendment to IFC Section 508
> 508.5.8 Fire Department connections. A fire hydrant shall be located within 
> 150 feet of all required and approved fire department connections.
>
> Regards,
>
> David M. Smith, Deputy Fire Marshal
> Vancouver Fire Department, Fire Marshal's Office
> 7110 NE 63rd Street
> Vancouver, WA 98661
> 360-487-7240 Phone/Fax
>
>
> ________________________________
>
> From: [email protected] on behalf of John Drucker
> Sent: Wed 4/8/2009 3:46 PM
> To: [email protected]
> Subject: RE: 100ft from FDC to hydrant?
>
>
>
> Members, Perhaps this will help;
>
> 2006 IFC Section 508 Fire Protection Water Supplies
>
> 508.5.1 Where required.
>
> Where a portion of the facility or building hereafter constructed or moved
> into or within the jurisdiction is more than 400 feet (122 m) from a hydrant
> on a fire apparatus access road, as measured by an approved route around the
> exterior of the facility or building, on-site fire hydrants and mains shall
> be provided where required by the fire code official.
>
> Exceptions:
> 1.      For Group R-3 and Group U occupancies, the distance requirement
> shall be 600 feet (183 m).
> 2.      For buildings equipped throughout with an approved automatic
> sprinkler system installed in accordance with Section   903.3.1.1 (NFPA-13)
> or 903.3.1.2, (NFPA-13R) the distance requirement shall be 600 feet (183 m).
>
> Don't forget about 2006 IFC Appendix B and C if adopted in your
> jurisdiction.
>
> Sincerely
>
> John Drucker
> Fire Protection Subcode Official
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to