I would always recommend asking for the reference when you receive comments and 
aren't sure where they are coming from. You'll want to make sure that you know 
what they are referencing and even that they have the ability to enforce it. 
 
For instance, portions of Chapter 5 of the 2006 IFC pertaining to fire 
department access weren't adopted at the state level and isn't enforceable in 
WA unless the local jurisdictions adopt it through local ordinance or have 
their own requirement. Other agencies may modify the model code with something 
more specific or restrictive. Our reference here in Vancouver would be:
 
Vancouver Municipal Code 16.04.160, Amendment to IFC Section 508
508.5.8 Fire Department connections. A fire hydrant shall be located within 150 
feet of all required and approved fire department connections.
 
Regards,
 
David M. Smith, Deputy Fire Marshal
Vancouver Fire Department, Fire Marshal's Office
7110 NE 63rd Street
Vancouver, WA 98661
360-487-7240 Phone/Fax

 
________________________________

From: [email protected] on behalf of John Drucker
Sent: Wed 4/8/2009 3:46 PM
To: [email protected]
Subject: RE: 100ft from FDC to hydrant?



Members, Perhaps this will help;

2006 IFC Section 508 Fire Protection Water Supplies

508.5.1 Where required.

Where a portion of the facility or building hereafter constructed or moved
into or within the jurisdiction is more than 400 feet (122 m) from a hydrant
on a fire apparatus access road, as measured by an approved route around the
exterior of the facility or building, on-site fire hydrants and mains shall
be provided where required by the fire code official.

Exceptions:
1.      For Group R-3 and Group U occupancies, the distance requirement
shall be 600 feet (183 m).
2.      For buildings equipped throughout with an approved automatic
sprinkler system installed in accordance with Section   903.3.1.1 (NFPA-13)
or 903.3.1.2, (NFPA-13R) the distance requirement shall be 600 feet (183 m).

Don't forget about 2006 IFC Appendix B and C if adopted in your
jurisdiction.

Sincerely

John Drucker
Fire Protection Subcode Official


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to