Listen to Steve but support it with the 2010 ROC.  We did a lot of  
work to explicitly address excessive clearance for spray sprinklers in  
storage under section 12.1.3.4 currently titled Ceiling Heights   
(changed that too).  The current criteria won't fly because it is  
limited to solid pile (as shown by the approach coming from the old  
NFPA 231) and Class I-IV in racks less than 25 ft (though that became  
clear only at the ROC).  Section 12.1 kills using it for all  
storage.   The option to put a barrier over the rack with sprinkler  
beneath them (tough option) was deleted.

Roland

On Apr 10, 2009, at 9:21 AM, Steve Leyton wrote:

> In-racks baby!   Sell sprinkers!
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA