It may be more cost effective to demo existing system and install new dry. 
The heads are 40 years old, pipe is sch 40 screwed...you'd save a lot on labor. 
Forest Wilson 

-----Original Message-----
From: Daniel Merkle <[email protected]>

Date: Sat, 11 Apr 2009 05:54:48 
To: <[email protected]>
Subject: Re: Storage Sprinkler


They are storing empty tin cans on pallets. (Primarily empty # 10 cans) Each 
pallet load is eight foot high. Then three loads stacked. The problem with this 
building is that it has an existing wet sprinkler system that was installed 
during the 60's. The building is a little over 23,000sqft. The owner would like 
to turn the system into a dry b/c of the heat bill during the winter months 
being over $10,000.00 a month. Have not been able to figure out what the 
original design intent, but the pipe sizing is out of control. Lots of 10", 8", 
5" and of course some 3 1/2". System would need to be split. Currently as one 
system would have a volume of over 2,100 gal.

 Daniel L. Merkle, CET 






________________________________
From: Todd Williams <[email protected]>
To: [email protected]
Sent: Friday, April 10, 2009 2:37:32 PM
Subject: Re: Storage Sprinkler

Just out of curiosity, what is the Class I product they are storing 
solid piled to 24'?



At 12:17 PM 4/10/2009, you wrote:
>Sorry, storage hight is 24'-0 which would give me 130% per 
>14.2.4.3.  My concern is the 38'-0" of open space to the roof.  What 
>if the roof was 100ft. high?
>
>  Daniel L. Merkle, CET
>
>
>
>
>
>
>________________________________
>From: Thom McMahon <[email protected]>
>To: [email protected]
>Sent: Friday, April 10, 2009 11:46:19 AM
>Subject: RE: Storage Sprinkler
>
>This is another "Outside the scope of NFPA 13" Situations. Obviously input
>from the sprinkler MFG.'s is good but they will be reluctant to take any
>design responsibility for conditions not defined by NFPA 13, or confirmed by
>testing. Time to hire a "Good" FPE.
>
>Even if you just look at Fig. 14.2.4.3, you'll see for 35 foot height you'd
>need over 200% design density if the graph even went that high. Then you
>have the additional problem of delayed response for the ceiling height
>outside of the scope. How do you allow for that? 2x or 3x the design area?
>You may even be looking at something other than "Control Mode" protection.
>Deluge? HE Foam? IR detection?
>
>Time for professional help outside of the "proscriptive Standard".
>
>Thom McMahon, SET
>Firetech, Inc.
>2560 Copper Ridge Dr
>P.O. Box 882136
>Steamboat Springs, CO 80488
>Tel:  970-879-7952
>Fax: 970-879-7926
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Daniel Merkle
>Sent: Friday, April 10, 2009 9:06 AM
>To: [email protected]
>Subject: Storage Sprinkler
>
>Anyone know of a storage sprinkler to protect a 62'-0" high building with
>solid pile Class 1 storage, stored to 36'-0"?
>
>Daniel L. Merkle, CET
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to