The last time I looked into fusible links for something like this I  
found they are typically not strong enough to carry much of a load and  
they are not created by top notch Italian industrial visual designers.  
In this case the interiors designer wants to support the fabric  
horizontally which means catenary style- flat. The flatter the  
catenary the larger the force. I have my doubts the designer  
understands the forces required. As for posing no threat, this is an  
early childcare center.

Allan Seidel
St. Louis, MO

On Apr 15, 2009, at 5:54 PM, Thom McMahon wrote:

> Since falling lycra fabric poses no threat to anyone below it, why not
> suggest installing fusible links on the fabric tension wires where  
> they meet
> the ceiling. They could be all on one side, which would allow the  
> fabric to
> hang straight down, or on all but one so the fabric would hang like  
> a drape,
> or on all wires, supposing that they will not all fuse at the same  
> time, and
> thus cover anyone making it difficult to exit.
>
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Allan  
> Seidel
> Sent: Wednesday, April 15, 2009 4:26 PM
> To: [email protected]
> Subject: Is there test information that shows whether or not  
> obstructing
> lycra fabric ceiling elements are an issue?
>
> The interiors architect plans to populate an open structure ceiling
> condition with many Lycra "kites" stretched horizontal at 11 foot in  
> an 18
> foot ceiling deck area above a light hazard space. The kite sizes  
> are many
> times larger than 48" and there are so many of these in an overlapping
> pattern that one cannot even start to argue that these are not gross
> obstructions. Conditions are such that is not possible to install  
> sprinklers
> underneath the fabric without penetrating vertically through the  
> fabric. The
> architect wants to convince the AHJ that the Lycra will "disappear"  
> in a
> fire condition, citing the fact that none of the product  
> installation photos
> show sprinklers. Is there test information that shows whether or not
> obstructing, horizontal Lycra fabric ceiling elements are or are not  
> an
> issue for sprinklers. One would assume such tests would indicate  
> fabric
> thickness, installed tension and other factors. This question will  
> be posed
> to the manufacturer. If anyone would know something about it, it is  
> probably
> someone on this forum. One can make up all sorts of plausible things  
> the
> Lycra might do in fire condition but nothing would compare to some  
> actual
> tests.
>
> Looking at this another way, is there merit in insisting the design  
> area be
> large enough to include all the kites in a plausible event area,  
> perhaps
> with a 30% penalty, and if so should the application rate be  
> increased? Is
> there supporting information for that line of thinking? It would be  
> nice to
> propose a defensible equivalency to the missing protection other  
> than sales
> brochures where the sprinkler protection has been photoshopped out.
>
> Allan Seidel
> St. Louis, MO
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to