This all begs a lot more questions: 1. Has this scenario be reproduced in a lab or other controlled environment? Full scale testing? 2. How does concentration impact reaction? 3. Was the antifreeze a pre-mix solution or mixed by the contractor? 4. Does the antifreeze and water separate over time? 5. If this is an issue, why hasn't NFPA been more proactive? 6. Glycerine vs. Propylene Glycol? 7. Does is react to flame or only a heat source?
At 03:02 PM 4/21/2009, you wrote: >Members, > >A settlement was reached in this matter. The public information that is >available is as follows; > >The area in question was a covered deck protected with sprinklers >utilizing antifreeze. At some point the deck was enclosed and heaters >added. Apparently the antifreeze and ordinary temperature sprinklers >remained. Heater operation resulted in sprinkler operation wherein a >"fireball" was described. > >John Drucker > > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of >[email protected] >Sent: Tuesday, April 21, 2009 2:39 PM >To: [email protected] >Subject: RE: antifreeze combustibility? > >It seems curious that there was an antifreeze system close to a unit >heater. If you have an antifreeze system it would seem you don't need >the heater and vice-versa. Hopefully the additional details to follow >will answer that question also. > > > >An incident related to antifreeze occurred at the WindanSea, Highlands, > > >NJ where a sprinkler system containing antifreeze discharged in > >proximity to a unit heater. The atomized liquid was ignited by the unit > > >heater and occupants burned from the fire that resulted. > >John Hoffman P.E. | Fire Protection Engineer | Facility Engineering >Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear >Security Administration's Kansas City Plant | Operated by Honeywell FM&T >| 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: >[email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) > >CONFIDENTIAL AND PROPRIETARY: >This email message is intended only for the use of the individual or >entity to which it is addressed and may contain information that is >privileged and confidential, nor is it, unless specifically stated, >intended to be relied upon by any person or persons other than the >individual or entity named above and no warranties or >representations are made or intended to persons or entities not >named above. If the reader is not the intended recipient, you are >hereby notified that any dissemination, distribution or copying of >this communication is strictly prohibited. If you have received >this communication in error, please notify us immediately by >telephone, return this message to the address above and delete all >copies. Thank you. > >_______________________________________________ >Sprinklerforum mailing list >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)