I don't see how a 10' deep box could not be a walk-in style.  There's two main 
problems.  The required slope of the shelves would drive the height of the box 
beyond 7' and loading the box from the front would very difficult to manage.  
It's too much weight to push.  It could be front loading from all 4 sides of 
the box.  Personally if you can walk inside, you need a sprinkler, otherwise 
it's really large furniture.  Also at 7' high it's likely the required 18" 
clearance isn't going to be met.

Jack Fairchild, CFPS  |  Fire Protection Designer  |  Ballinger  |  v 
215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  Suite 1400    
Philadelphia, PA   19107  |  www.ballinger-ae.com


George,

I don't recall it being described as "big insulated panel box.' In
fact I think Tony said he hadn't seen it. Go back a post or two. My
thought is that if this thing is a factory manufactured device  that
is brought out on a truck, dropped off and plugged-in (even if it
comes in large sub-assemblies that just plug into each other) then
it's a big reefer and not a room or space.

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)