You are correct, industrial ovens where pre-heated, high pressure oil is 
present requires sprinklers as do some flammable liquid storage cabinets.  This 
is neither of those.


From NFPA 13, 2007:

(7) Furniture, such as portable wardrobe units, cabinets, trophy cases, and 
similar features not intended for occupancy, does not require sprinklers to be 
installed in them. This type of feature shall be permitted to be attached to 
the finished structure.

Jack Fairchild, CFPS  |   Fire Protection Designer  |  Ballinger  |  v 
215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  Suite 1400    
Philadelphia, PA   19107  |  www.ballinger-ae.com<http://www.ballinger-ae.com>
larryshulman larryshulman at earthlink.net 
<mailto:sprinklerforum%40firesprinkler.org?Subject=Walk-in%20cooler&In-Reply-To=44587969A9EB6A458C2664D74F80F9FB3D57B6D1%40mail-3>
Fri Apr 24 15:10:01 CDT 2009


I'm confused how if the space is inhabitable should be a criterion for

installing sprinklers.  After all, sprinklers are installed inside

industrial ovens and flammable liquid storage cabinets all the time.  Nobody

in this discussion thread has asked if the cooler construction warrants the

installation of sprinklers.  Although the surface of the cooler walls and

ceiling may be metal lined, what happens if it is exposed to heat, warps,

and exposes the foam insulation beneath?  That's why UL Listed or FM

Approved panels need to be used, to ensure the construction materials don't

contribute to the fire load.



-----Original Message-----

From: sprinklerforum-bounces at 
firesprinkler.org<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>

[mailto:sprinklerforum-bounces at 
firesprinkler.org<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>]
 On Behalf Of Fairchild,

Jack

Sent: Friday, April 24, 2009 11:13 AM

To: sprinklerforum at 
firesprinkler.org<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>

Subject: RE: Walk-in cooler



I don't see how a 10' deep box could not be a walk-in style.  There's two

main problems.  The required slope of the shelves would drive the height of

the box beyond 7' and loading the box from the front would very difficult to

manage.  It's too much weight to push.  It could be front loading from all 4

sides of the box.  Personally if you can walk inside, you need a sprinkler,

otherwise it's really large furniture.  Also at 7' high it's likely the

required 18" clearance isn't going to be met.



Jack Fairchild, CFPS  |  Fire Protection Designer  |  Ballinger  |  v

215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  Suite 1400

Philadelphia, PA   19107  |  www.ballinger-ae.com





George,



I don't recall it being described as "big insulated panel box.' In

fact I think Tony said he hadn't seen it. Go back a post or two. My

thought is that if this thing is a factory manufactured device  that

is brought out on a truck, dropped off and plugged-in (even if it

comes in large sub-assemblies that just plug into each other) then

it's a big reefer and not a room or space.



_______________________________________________

Sprinklerforum mailing list

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: techsupport at 
firesprinkler.org<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>



To Unsubscribe, send an email to:Sprinklerforum-request at 
firesprinkler.org<http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum>

(Put the word unsubscribe in the subject field)



________________________________
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to