Really? Do medical levels apply to a dry system central air system? I suppose I can see as it might but a separate system? They have hospital grade medical air/vac/etc. This is the building I wrote about months ago with the 22 dry valves and 16 riser-mounted compressors. I bought an 8 HP gas driven air compressor to help with the valves and we kept setting off the co sensors. :P I was thinking a house system might be the way to go, we wouldn't be running though any medical floors. Tom
Tom: Check NFPA 99 4-3.1.1.9 medical air comp supply systems, and table 4-3.1.2.4 and table 4-3.1.2.7 as well as the medical facility people JACHO and AIA, look at NFPA 99C Level three comp gas system, and don't forget oil free, and filter and receiver requirements. PS your liability insurance may not cover this type of work. Thom McMahon, SET Firetech, Inc. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)