I'm going to go out on a limb and say I don't think the group  
interpreted your initial question as being a separate air supply.  So  
how about repeating the question?

Roland

On May 20, 2009, at 6:44 PM, Tom Duross wrote:

> Really?  Do medical levels apply to a dry system central air system?
> I suppose I can see as it might but a separate system?  They have  
> hospital
> grade medical air/vac/etc.
> This is the building I wrote about months ago with the 22 dry valves  
> and 16
> riser-mounted compressors.
> I bought an 8 HP gas driven air compressor to help with the valves  
> and we
> kept setting off the co sensors.  :P
> I was thinking a house system might be the way to go, we wouldn't be  
> running
> though any medical floors.
> Tom
>
>
>
> Tom:
>
> Check NFPA 99 4-3.1.1.9 medical air comp supply systems, and table  
> 4-3.1.2.4
> and table 4-3.1.2.7 as well as the medical facility people JACHO and  
> AIA,
> look at NFPA 99C Level three comp gas system, and don't forget oil  
> free, and
> filter and receiver requirements.
>
> PS your liability insurance may not cover this type of work.
>
> Thom McMahon, SET
> Firetech, Inc.
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to