If all it runs is non-medical equipment, and it is properly labeled (every 5'-0") so in the future it will not mistakenly be used for medical equip. I see no problem. This would not need to meet medical gas requirements, but still there may be Jahoe or other state medical facilities requirements that it must meet. Like: "All non-medical compressed air pipe must be painted blue" or "All non-medical compressed air shall be labeled ever 2 feet with lettering a minimum of 1/2" HIGH "NON-MEDICAL COMPRESSED AIR, NOT FOR CONNECTION TO MEDICAL EQUIPMENT"
Just be careful. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tom Duross Sent: Wednesday, May 20, 2009 7:44 PM To: [email protected] Subject: RE: Compressed Air Piping Really? Do medical levels apply to a dry system central air system? I suppose I can see as it might but a separate system? They have hospital grade medical air/vac/etc. This is the building I wrote about months ago with the 22 dry valves and 16 riser-mounted compressors. I bought an 8 HP gas driven air compressor to help with the valves and we kept setting off the co sensors. :P I was thinking a house system might be the way to go, we wouldn't be running though any medical floors. Tom Tom: Check NFPA 99 4-3.1.1.9 medical air comp supply systems, and table 4-3.1.2.4 and table 4-3.1.2.7 as well as the medical facility people JACHO and AIA, look at NFPA 99C Level three comp gas system, and don't forget oil free, and filter and receiver requirements. PS your liability insurance may not cover this type of work. Thom McMahon, SET Firetech, Inc. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)