Another option is to not run the pump at 150%

Roland

On May 26, 2009, at 5:59 PM, Todd Williams wrote:

> The pump is a 250 gpm; a minimum of 4" suction is required (OK,
> 3-1/2). I did a project with the same size pump 2 years ago, taking
> suction from 2 tanks with a 4" suction line. When we tested the pump
> at 150%, we drew the suction down to -1 psi. There is going to be
> more suction pipe on this than the last, so I told them to use 6"
> because I was afraid that the suction would go below -3 psi at the
> acceptance (per 5.14.3.2). So the 6" sizing was my doing for those
> reasons. I provided the tank and suction pipe sizing and the rest of
> the design is up to others. We also cannot increase the size of the
> pump, as someone suggested because we only have single phase power
> and 250 gpm at 60 psi is the largest we can get.
>
> I am now finishing up the final piping arrangement for the pump and
> was questioning the reducer arrangement.