Thanks Matt, I'd already read that in the 2007, and was hoping for more. On another note, it is my understanding that section 8.15.1 Concealed Spaces (8.14.1, 2002) is in regard to exposed combustible construction only. This includes all of the following paragraphs in this given section. Is this correct? If correct, then the text in 8.15.1.1 that states, "Concealed spaces enclosed wholly or partly by exposed combustible construction shall be protected by sprinklers" would then dictate to me that the noncombustible concealed space in this attic does not require sprinklers. Right? But, what about the next two sections that are in regard to noncombustible and limited combustible materials? How do these two sections fit within the entire section that is speaking about combustible construction? Thanks for the help; I'll have to continue this tomorrow. I have a baseball game to go to right now.
Bob -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matthew J. Willis Sent: Thursday, May 28, 2009 3:45 PM To: [email protected] Subject: RE: Definition of Throughout Bob, See 8.1 and the annex (02) Matt Matthew J. Willis, CET Automatic Fire Sprinklers Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Knight Sent: Thursday, May 28, 2009 4:41 PM To: [email protected] Subject: Definition of Throughout I was just handed a situation where a H&W plans examiner is citing the term "throughout" to mean that sprinklers are required in a non-combustible attic space. His reasoning varies from the presence of HVAC, electrical, catwalks, etc... Can anyone provide me with a definition for the wording "throughout" as found in NFPA 13? Thanks, Bob Knight, CET (208) 318-3057 [email protected] www.firebyknight.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)