Thanks Matt,
I'd already read that in the 2007, and was hoping for more.  On another
note, it is my understanding that section 8.15.1 Concealed Spaces (8.14.1,
2002) is in regard to exposed combustible construction only.  This includes
all of the following paragraphs in this given section.  Is this correct?  If
correct, then the text in 8.15.1.1 that states, "Concealed spaces enclosed
wholly or partly by exposed combustible construction shall be protected by
sprinklers" would then dictate to me that the noncombustible concealed space
in this attic does not require sprinklers.  Right?  But, what about the next
two sections that are in regard to noncombustible and limited combustible
materials?  How do these two sections fit within the entire section that is
speaking about combustible construction?  Thanks for the help; I'll have to
continue this tomorrow.  I have a baseball game to go to right now.

Bob


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matthew J.
Willis
Sent: Thursday, May 28, 2009 3:45 PM
To: [email protected]
Subject: RE: Definition of Throughout

Bob,
See 8.1 and the annex (02)

Matt

 
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Thursday, May 28, 2009 4:41 PM
To: [email protected]
Subject: Definition of Throughout

I was just handed a situation where a H&W plans examiner is citing the term
"throughout" to mean that sprinklers are required in a non-combustible attic
space.  His reasoning varies from the presence of HVAC, electrical,
catwalks, etc... Can anyone provide me with a definition for the wording
"throughout" as found in NFPA 13?

Thanks,

Bob Knight, CET
(208) 318-3057
[email protected]
www.firebyknight.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to