NFPA 13, 2007
8.1.1 (1) REQUIRES SPRINKLERS THROUGHOUT

A.8.1.1 This standard contemplates full sprinkler protection
for all areas including walk-in coolers, freezers, bank vaults,
and similar areas. Other NFPA standards that mandate sprinkler
installation might not require sprinklers in certain areas.
Based upon experience and testing, sprinklers have been
found to be effective and necessary at heights in excess of 50 ft
(15.2 m). For a building to meet the intended level of protection
afforded by NFPA13, sprinklers must not be omitted from
such high ceiling spaces. The requirements of this standard
should be used insofar as they are applicable. The authority
having jurisdiction should be consulted in each case. A building
is considered sprinklered throughout when protected in
accordance with the requirements of this standard.


IFC
903.3.1.1 NFPA 13 sprinkler systems. Where the provisions
of this code require that a building or portion
thereof be equipped throughout with an automatic sprinkler
system in accordance with this section, sprinklers
shall be installed throughout in accordance with NFPA
13 except as provided in Section 903.3.1.1.1.
903.3.1.1.1 Exempt locations. Automatic sprinklers

903.3.1.2 NFPA 13R sprinkler systems. Where
allowed in buildings of Group R, up to and including four
stories in height, automatic sprinkler systems shall be
installed throughout in accordance with NFPA 13R.
903.3.1.2.1 Balconies and decks. Sprinkler protection

903.3.1.3 NFPA 13D sprinkler systems. Where
allowed, automatic sprinkler systems installed in oneand
two-family dwellings shall be installed throughout
in accordance with NFPA 13D.
903.3.2 Quick-response and residential sprinklers.

This was just to show that "Throughout" means different things in different
parts of the code. Also there are many "Exceptions" in the IFC to what shall
be sprinklered, one exception is a non-combustible room with non-combustible
contents. If you're not required to protect a non-combustible occupiable
room, why would you be required to protect a non-combustible concealed space
above that room?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Thursday, May 28, 2009 3:41 PM
To: [email protected]
Subject: Definition of Throughout

I was just handed a situation where a H&W plans examiner is citing the term
"throughout" to mean that sprinklers are required in a non-combustible attic
space.  His reasoning varies from the presence of HVAC, electrical,
catwalks, etc... Can anyone provide me with a definition for the wording
"throughout" as found in NFPA 13?

Thanks,

Bob Knight, CET
(208) 318-3057
[email protected]
www.firebyknight.com


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to