Echo what Craig said. From memory I believe that one trigger is over
40ft and enclosed. In that condition they are almost always covered. As
others have said there is some ambiguity here but the underwriter
usually has the most input.

Rod DiBona
Rapid Fire

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Friday, June 26, 2009 6:45 AM
To: [email protected]
Subject: RE: Conveyor Sprinklers

There are a lot of factors involved in making the determination.  

Belt material - combustible or non-combustible

Enclosed or open - enclosed are almost impossible to fight with hose
stream attack if not protected internally.

High elevation - again, another hose stream and access issue.

Value and importance to client - if the conveyor is handling combustible
material and/or is of a combustible composition, and/or is of high value
to the overall production of the plant site then it should be protected.
Ask this question, if the conveyor was destroyed, would it significantly
impact production?

Any Underwriter requirements?

Any local AHJ/FD requirements? 

Any owner Loss prevention requirements?

There is plenty of data between NFPA and FM on how to protect them.  The
IFC has some direction for requirements of various types but not all
types.  These are some of the questions I'd be asking the client and
other in order to make that determination if your particular conveyor
type isn't mentioned in the IFC. 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay White
Sent: Thursday, June 25, 2009 4:56 PM
To: [email protected]
Subject: Conveyor Sprinklers

Do all conveyors require a water spray fixed system as addressed in NFPA
15?


Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to